inova

join:2006-05-03
Macnutt, SK

Grounding test

I did find this post: »Re: New set-up for base of tower (was Managed Switch (again))

But, I don't have access to a megger. Is there some way I can test the grounding on a 50' tower other than cooking multiple radios? There must be grounding issues at this farmyard site. They talk about their vhf radio behaving oddly and excess corrosion on copper plumbing.


superdog
I Need A Drink
Premium,MVM
join:2001-07-13
Lebanon, PA

said by inova:

Is there some way I can test the grounding on a 50' tower other than cooking multiple radios?
If You were to take a multi-meter with very, very long leads, You MAY be able to test resistance from the top of the tower to bottom?
--
»www.wavecrazy.net Join WISPA today! »www.wispa.org/

inova

join:2006-05-03
Macnutt, SK

I thought about that, and had planned on checking section to section continuity. But I am guessing if there is a problem it will bad or corroded ground rod. Can you think of a way to check that without a megger?


slipstream1
Premium
join:2005-11-15
Jacksonville, TX

reply to inova
To get a true picture of resistance to ground you need a megger. You could do a check on the ground leads with a amp clamp and see if there is any stray current running on the ground leads. If so, I would try to eliminate that first.


lutful
Premium
join:2005-06-16
Ottawa, ON
Reviews:
·TekSavvy DSL

said by slipstream1:

To get a true picture of resistance to ground you need a megger.
We had an antique mahagony megger in our high school physics lab that we used for head-to-toe measurements.

I wanted to understand how a "mega-ohm" measuring tool helps to measure "sub-ohm" resistance of most grounding systems.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:3

reply to slipstream1

said by slipstream1:

To get a true picture of resistance to ground you need a megger. You could do a check on the ground leads with a amp clamp and see if there is any stray current running on the ground leads. If so, I would try to eliminate that first.
The easiest way to check it (without instrumentation) is to disassemble and clean all of the connections. This should be part of a semi-annual preventative maintenance program for the tower. Do it once in the fall before the snow flies, and once after the spring thaw (if you have that kind of weather).

Any type of corrosion is bad. You mention that this is at a farmyard. Farmyards typically have a higher concentration of ammonia and sulfides...both of which are corrosive. You want to see bare, bright copper. Wire brushes work well if used cautiously (so as not to remove too much copper). Chemical cleaners can be use but require knowledge of how they work so you do not cause the very problem that you are trying to avoid. After cleaning, use an anti-oxidation compound like No-AlOx on the connections. A light coating is all that is needed. "Too much" is too much.

Eliminate any iron/steel screws bolts in the grounding hardware and replace them with stainless hardware. Make sure all the connections are tight, but not over-tight. Over-tightening increases the resistance of the connection.

As Slipstream pointed out, you may have unwanted AC currents flowing in your grounding system. This is especially true if the power is supplied from a building some distance from the tower as opposed to a separate service at the tower. A high impedance ground fault can let current flow without tripping the breaker. His suggestion of using an amprobe to detect the current is a good one. Most digital amprobes can resolve to the tenths of an amp.

It may be a "grind" to deal with this the first time, but it will be easier to do the next time. Grounding systems can turn to crap if neglected...so don't do that.


--
A is A

slipstream1
Premium
join:2005-11-15
Jacksonville, TX

Or you can eliminate the mechanical connections of the tower completely by using a down conductor that is attached to tower ground field. If you suspect that the connections, on the tower are corroded, this may be a good quick test. If you disassemble be sure to use some sort of non-oxydizing compound to slow down corrosion between parts that would need a excellant electrical connection.


lutful
Premium
join:2005-06-16
Ottawa, ON
Reviews:
·TekSavvy DSL

reply to inova

said by inova:

section to section continuity
is difficult to test.

But really, the whole tower should be treated as the test electrode for a IEEE 81 test. That is the only way to be sure it is less than one ohm to ground.

said by inova:

I am guessing if there is a problem it will bad or corroded ground rod.
Either visual check as John suggests ... or ....

Apply a nanosecond kilovolt pulse to tower-top at night. Radios will not be damaged at all if they have even basic surge protection, but there will be visible arcing at corroded joints or loose plates.

There is a commercial tool from Sandia Labs for airplane cable testing but I forgot the name. But I am sure it will cost $$$$$.

said by inova:

Can you think of a way to check that without a megger?
The original "megger" was for mega-ohm insulation testing, not for "sub-ohm" ground testing. But I just found out that Megger is now a brand-name and they do make dedicated ground testers.

But you can use any brand really, no need for a Meggar brand. I like AEMC surplus catalog but you could rent them at Electro Meter in Toronto and other places near you.

Wireless Dav

join:2005-10-22
Divernon, IL

reply to inova
I think that it is best to divide what has been discussed in this thread into two items to be tested. One thing is the resistance from whatever is at the top of the tower, to the bottom of the tower. The other thing to be tested is the resistance between the bottom of the tower and the earth.

When testing the resistance between tower sections there is no need for a megger. A megger is used when testing insulation or anything else that won't conduct well at low voltages. If you test insulation (like the insulation on a motor winding) with a common multimeter, it SHOULD read like an open circuit. If you use a megger on the same insulation it will typically generate about 500V (or whatever you set it at) and the higher voltage will likely get some measurable current to flow. This current flow will typically register as a reading in the Mega-ohm range. If this higher voltage is necessary to get current flow between tower sections, you have some serious issues. The connections between tower sections should not require any significant voltage to get current to flow. A standard multimeter is adequate for the test. If you want to test the connection more accurately, you can use a digital low resistance ohmmeter. They clamp to the two sections to be tested and inject up to 10A and then check to see what voltage is generated as a result of the current. These meters have great resolution at the hopefully low resistance range between the tower sections. It could easily be argued that the meter would not be so practical for towers because they usually have leads 30 feet or less and they are pretty heavy units.

To measure the connection of your tower to earth, ideally you would use a ground resistance tester. It uses one or more probes or you could think of them as test ground rods. If you are getting the corrosion on the tower ground rods like they report happens to copper plumbing, this tester would show that.

If you don't want to get a ground resistance tester, you can do a crude but effective test with a standard multimeter and a couple of ground rods. Drive one of the ground rods maybe three feet out from the tower ground rod(s) and then the other ground rod the same distance further out. Measure the resistance from the tower to the first ground rod and compare that to the resistance between the two test ground rods. The two readings should be in the same ball park. If the reading from the tower to the first ground rod is significantly higher than the reading between the two test ground rods, you have found a problem with the grounding of the tower to earth.

Sorry for the long post. Hope it helps.


inova

join:2006-05-03
Macnutt, SK

I think we found it. With my ohm meter I could get a measurement 1400 ohms from the ground rod to a reference rod. I got 150 ohms from the reference to my probe in the ground only 1 inch deep (same distance apart). We dug up around the ground rod 6" deep or so and I could see no evidence of galvanization at all only corrosion. I had to file the top of the rod off just to make probe contact. It was enough to convince him (and me) his ground rod was a dead duck. He is off to purchase a shiny new one. I realize this is rudimentary testing but it still seemed pretty obvious to me. Thanks Wireless Dav and everybody.



John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:3

said by inova:

We dug up around the ground rod 6" deep or so and I could see no evidence of galvanization at all only corrosion. I had to file the top of the rod off just to make probe contact.
Why did it corrode so much?

Some soil types react with the ground rods. You might try another type. Usually the local electricians or stores will be aware of the problem and can steer you to the right type for your area.

We have that problem here in Oregon...we use galvanized rods instead of copper-clad.

You still should check to see if there is any current flowing...that still might be an issue.
--
A is A

inova

join:2006-05-03
Macnutt, SK

Typical farmer (oops did I say that out loud?), the rod was probably in the ground for 20 or 30 years and it was a salvaged rod when he put it in (his confession). It may have indeed been copper clad but I can't say for sure. I rounded up a shiny new galvanized one and just got home from installing it. The measurements I could make with my ohm meter (to a makeshift reference) went from 1400 ohms to about 8 to 50 ohms, a marked improvement. It did seem to do some hunting in that range as if there was some capacitance involved but none the less much better. It is currently very dry here, that probably has something to do with it also. I installed a ups and when the wind dies down I will climb up and install delib2315 #3. Fingers crossed... It is costly but I am learning things and I like that.



electric6

@sbcglobal.net


But I am guessing if there is a problem it will bad or corroded ground rod.
A single ground rod is not adequate. You need at least three rods for a meaningful lightning protection ground.


It did seem to do some hunting in that range as if there was some capacitance involved but none the less much better
A DC meter reading will drift because of electrolysis.


Splitpair
Premium
join:2000-07-29
Cow Towne
kudos:3

reply to inova
I would avoid galvanized ground rods as they can develop high resistance due to interaction with chemicals in the soil. If copper plated rods are not holding up switch to stainless steel. While a galvanized rod might measure low resistance with a VOM under high current from a strike it may fail to provide a good connection to earth.

Avoid using any type of clamps or crimp type connecting devices on your ground system. Connections should be made with exothermic welds only. If you are only doing a few systems then the Cadweld one shot system is they way to go.

Also where you place your ground rods install a small round 12 inch or so sprinkler housing with a removable lid over the rod. This will provide ready access to both the top of the rod and the weld for easy inspections and testing plus because the housing can be seen from ground level it may help prevent the rod and connection from being damaged by other contractors.

Wayne
--
If you cannot fix it with a buttset and some beanies you ain't a technician.


Stealthwave

join:2005-07-03
Alvin, TX

Would one of these units be good and if so witch one is better to have?
ECOS 2167 MEGGER FRAME GROUND MONITOR RESISTANCE TESTER
AEMC Ground Soil Resistance Tester 3640



UHF
All static, all day, Forever
Premium,MVM
join:2002-05-24
Reviews:
·Callcentric
·DIRECTV
·surpasshosting
·Dish Network
·VOIPo

reply to inova
Why was there only one rod?? Even the safety ground on a house needs a minimum of two 8' ground rods. If you are only going to put in one ground rod, then why bother at all? Drive in AT LEAST two more, a minimum of 16' apart, and bond with #2 copper wire or larger. Yes, it's a pain in the ass, but it will save your equipment.

I've spent the last 12 years working around tall towers, I've seen the difference between good grounding and poor grounding. My 2000' foot(yes, I said two-thousand feet) tower was struck by lightning twice this morning on my drive in, no damage to anything when I got here. That's the beauty of a good grounding system.


inova

join:2006-05-03
Macnutt, SK

Yes I already pointed that out to the customer and he said he would install them but I am sure it will take some prodding.

2000'! Cool! Can you post a pic? Can I come climb it and check out the view? Better yet, do you have any pics from the top of that puppy?



Splitpair
Premium
join:2000-07-29
Cow Towne
kudos:3

said by inova:

Can I come climb it and check out the view? Better yet, do you have any pics from the top of that puppy?
At 2Kf I would hope it has a man-lift.

Wayne
--
If you cannot fix it with a buttset and some beanies you ain't a technician.


UHF
All static, all day, Forever
Premium,MVM
join:2002-05-24
Reviews:
·Callcentric
·DIRECTV
·surpasshosting
·Dish Network
·VOIPo

said by Splitpair:

At 2Kf I would hope it has a man-lift.
Yes, it does, but the last 200 feet or so you have to climb the pole. That last light bulb is a real b*tch. I don't climb, we contract out all the tower work.

slipstream1
Premium
join:2005-11-15
Jacksonville, TX

reply to Stealthwave
AEMC is the best units that you can buy. I believe that we have the 3500 series units.