Search:  

 
 
   All ForumsHot TopicsGallery






how-to block ads


 
Forums » Tech and Talk » Technical » Ham Radio » The Science of Effective Grounding...
Search Topic:
Share Topic:
RSS topic:
toggle:
flat / full
normal / watch
Posting:
Post a:
Post a:
Yaesu FT-747GX »
« Impedance 101: A Refresher on Transmission Lines & Cable Ind  
AuthorAll Replies


KA3SGM
- -... ...- -
Premium
join:2006-01-17
West Chester, PA
clubs:
·Verizon FIOS

reply to burner50
Re: The Science of Effective Grounding...

said by burner50 See Profile :

Guess i never consulted the NEC...

never heard of that either...

We put in a similar field at my last job except we used 24 rods, but this was for a freestanding structure not an aerial antenna.

Edit: A 15x15 structure with about 20 million worth of electronic equipment
I think the NEC intent is that a 6 foot spacing between ground rods that are bonded together comprises two separate ground points.

Anything closer than 6 foot is obviously better than a single ground rod, but a cluster of closely spaced rods is considered a single ground point, the 6 foot spacing compensates for differential from one ground point to another.

Many commercial sites have several ground 'test wells' to determine the ground potential differential between different points at the same site.

Still, everything metal above ground is bonded to everything else, and all ground rods are bonded to each other.

This includes towers, buildings, antennas, feedlines, power and telco demarks, even the security fencing.

Everything metallic is connected to ground, and all ground points are bonded to each other.

Ideally, Lightning/Static/EMP flashes over the site uniformly, and finds an effective ground anywhere it touches.

At least that is the theory behind it, not that it always works that way.

Of course when you have 7 to 8 $ figures worth of electronics sitting on the ground, you do what you can to keep everything at an even ground potential, so nothing gets singled out to be 'THE' ground rod.
--
"Lithium is no longer available on credit"


Splitpair
Premium
join:2000-07-29
Cow Towne
·T-Mobile US
·T-Mobile US
·AT&T Southeast

Click for full size
said by KA3SGM See Profile :

I think the NEC intent is that a 6 foot spacing between ground rods that are bonded together comprises two separate ground points.
With widely spaced rods connected by the proper gauge bond wire an additional rod would halve the resistance under load of the first one a third rod would bring at all down to a third a fourth to a fourth and so on to the point of a diminishing return. However with close spacing such as 6 foot with average soil resistance/moisture the second rod will only lower the resistance under load by about 66% a third rod will make it 40% and the forth 33%.

To get a better understanding think of a ground rod as an antenna turned upside down and shoved into the earth. When passing power to earth the energy leaves the rod and spreads out in all directions from the rod producing a voltage gradient around the rod. If another bonded rod is too close its voltage gradient comes up against the other rods gradient reducing the effects of multiple rods.

The potential in volts per inch/foot varies by soil resistance and soil makeup. Generally speaking moist sandy soil will have the lowest resistance producing tight gradients and good protection.

Wayne
--
If you cannot fix it with a buttset and some beanies you ain't a technician.
Forums » Tech and Talk » Technical » Ham RadioYaesu FT-747GX »
« Impedance 101: A Refresher on Transmission Lines & Cable Ind  


Tuesday, 02-Dec 02:53:57 Terms of Use | Privacy Policy | Hosting by www.nac.net - DSL,Hosting & Co-lo | feedback | contact
over 9 years online! © 1999-2008 dslreports.com.
page compression OFF
Most commented news this week
· [94] AT&T Metered Billing Trial Hits Second Market
· [69] UDP BitTorrent Will Destroy The Interwebs!
· [57] Comcast Tries To Slow Verizon's Philly Entry
· [17] FCC To Vote On Free National Wireless Broadband
· [14] Clearwire May Slow WiMax Build
· [7] Hawaii Telecom Files For Bankruptcy
· [6] Embarq Rejected Higher Offer
· [5] Monday Evening Links
Most people now reading
· Is this a good thing for the net? [news,99366]
· Upverting DVD players vs Blue ray DVD players. [General Questions]
· Level 80 PVP gear info? [World of Warcraft]
· Maintaince Tonight or tomorrow? [TekSavvy]
· Coalition Government Possible? [TekSavvy]
· Notice, new uTorrent Alpha may be able to evade throttling [TekSavvy]
· Java SE Runtime Environment (JRE) 6 Update 11 [Security]
· [Rant] Black Friday Deaths [Rants, Raves, & Praise]