Hi folks,

I have a question about home A/C. From the point where the transition from the coil meets the plenum, how far down the plenum should the first ducts be?

In mine, we have a brand-new a/c system (less than four years old) but the plenum and ductwork is the original 40+ hardpipe (recently sealed and reinsulted by me). The unit is in the attic, and there are two 10" ducts about a foot or so from the transition - directly opposite each other. Is that too close?

They supply three bedrooms and two bathrooms on the east side of the house and have never seemed to have the same robust airflow as the other ducts that supply the rest of the house. The first of those ducts start about 7-8 feet away from the transition. As a result, the east side of the house is always a couple of degrees warmer or cooler than the rest of the house.

I'm wondering if we should reroute those two ducts so they connect to the plenum farther on along. There is plenty of access so it that wouldn't be a problem. I just don't want to do it if it's not going to solve anything.

Does anyone have any advice?

Thanks!

wig

PS I'll try and get a photo at lunchtime.


jack b
Gone Fishing
Premium,MVM
join:2000-09-08
Cape Cod
kudos:1

The airflow is always going to take the path of least resistance, so closer takeoffs will usually get a better blow, unless they have a high resistance built in due to design.
The system can deliver X amount CFM, and it all has to go someplace.
Manual dampers are the best way to balance branches off the main trunk. Moving the take off point further down makes no sense.
--
~Help Find a Cure for Cancer~
~Proud Member of Team Discovery ~


averagedude

join:2002-01-30
San Diego, CA

jack b is correct.
Air likes the path of least resistance.
All the balancing dampers do is increase resistance so that the air would rather go somewhere else.


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

1 edit

reply to emptywig

Click for full size
Coil, Transition and Plenum with First Duct
Click for full size
Looking Further on Down the Plenum
Thanks for your answers.

My thoughts were that with those ducts being so close to the blower that the air would blow past it, and once the system equalized in pressure that the turbulence at that point might impede the airflow to those ducts.

DISCLAIMER - I AM NOT AN A/C PERSON - just an average dude!

So maybe there too many branches off of those two ducts? WOuld I do better to run each to the plenum separately? Does a 6'x12' bathroom NEED a 6" supply?

Like I said, the rest of the ducts in the house work brilliantly.

Thanks again,

wig

robbin
Premium,MVM
join:2000-09-21
Leander, TX
kudos:1

The 10" supply ducts are too small for the ducts they are feeding. In the first case you have a 10" feeding two 7" and one 5". Calculating cross sectional area using the formula pi2r you find the following.

10" ~ 33 square inches
7" ~ 21
5" ~ 15

So you have 33 square inches feeding 57 square inches.

In the second case you have a 10" duct feeding an 8" and a 6" - so

10" ~ 33 square inches
8" ~ 24
6" ~ 18

In this case you have 33 square inches feeding 42 square inches.

In both cases the 10" duct is too small for what it is feeding.


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

reply to emptywig
Maybe they didn't do very much math in the early sixties

Looks like I have a little rearranging to do.

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."



SandShark
Long may you run
Premium,MVM
join:2000-05-23
Santa Fe, TX
kudos:3

said by emptywig:

Maybe they didn't do very much math in the early sixties

Looks like I have a little rearranging to do.

wig
Duct design is not as simple as calculating square inches of ducts. One cannot, based on those calculations, determine whether or not a branch duct that is supplying a mixing box that is supplying two other ducts is sufficient without knowing room loads, blower data (CFM), duct lengths/sizes, static air pressure drops, fittings, etc. Not only that, there may be other factors that are affecting how the system is performing.

You mention the system is less than four years old, but the duct system is "the original 40+"? I take that to mean the duct system is 40+ years old? If that is the case, there's a good chance the duct system was originally designed for heat only. Did the company that installed the system perform a Manual J load calculation on the home. Did they ensure the existing duct system was designed and sized for the system according to Manual D Duct Design? Was the duct system balanced? Living in Texas, living in the general vicinity of Pasadena, working in HVAC for 25+ years, and knowing a little about how some companies in this area operate, I get the impression that some shortcuts may have been taken with the installation of this system. Correct me if I'm mistaken.
--
• • • - - - • • • | Hunt's Treasure

emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

1 edit

There were no shortcuts (it took a full week in the middle of summer) except that we couldn't afford to have them strip/seal/reinsulate the old ductwork. I have been doing that bit-by-bit in the couple of years since then.

The system was installed by Central City Air, and has been spectacular. They did all the calculations, and initial inspections, and they recommended we keep the old ductwork. They were impressed that it had dampers installed. We even added two more ducts and a return air on the far end of the house, and a fresh-air return.

You're correct, the original ductwork was probably for heating only. Some of it was not even connected with screws - just pressed together.

But the airflow problem predated this system. It has always been a problem on that side of the house, and that side has always been fed by those two 10" pipes. All of the other rooms are fed by ducts that connect directly to the main plenum.

I have no complaint about the way the system performs. My electricity bills are lower by a third. There is no problem getting the house either cool or heated. The humidity is rock-solid at 50% during the most humid days , and there is plenty of extra overhead for really hot days. And the imbalance is not really even that great - 1 to 2 degrees. Still, if its something I could sort out pretty easily, I'd like to.

Thanks,

wig

PS I met all of the goombah A/C guys while I was getting my estimates.

--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

Oh, sorry - yes, the ductwork is 40+ years old.

wig



SandShark
Long may you run
Premium,MVM
join:2000-05-23
Santa Fe, TX
kudos:3

reply to emptywig
I'm very familiar with Central City Air. I should have known when I saw that two-staged evaporator coil. Oh, well, maybe you should call them and have that air balance problem taken care of. Good luck!
--
• • • - - - • • • | Hunt's Treasure



jig

join:2001-01-05
Hacienda Heights, CA

reply to emptywig
if you already have dampers installed, couldn't they be set incorrectly?

other than adjusting those, you are probably stuck adjusting the registers to try to generate some back pressure (and i think this is generally frowned upon).

the problem could be, if your house is sealed well enough, that you have pressures inside the house working against your distribution scheme. probably hard to fix even with dampers, and maybe exacerbated by the return duct added recently.


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

reply to SandShark
I'm still smarting from their first bill. Followed the very next year by a new roof. Do you think I play with hardcast and duct insulation for fun? LOL.

Like I said, this is not one of those things that keeps me up nights. But I've been putting radiant barrier up in the attic while its been cool, and you know, you just start looking at things and wondering...

Thanks again.

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

reply to jig
Its not exactly what I'd call a tight house. Its a ranch from the 50's, original aluminum windows. Can you explain a little what you mean? I was under the impression that in a tighter house, return air and a fresh-air return were even more important.

It could be the dampers. I've just been hesitant to adjust any of them too much for fear of messing up the excellent results in the rest of the house without actually fixing the slight problem in that one area. I don't generally like to fiddle with things that 1) are working more or less fine and 2) I don't really know much about. I know just enough to be dangerous.

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."



jig

join:2001-01-05
Hacienda Heights, CA

on the return duct issue, the rooms closest to the return will have the lowest air pressure, especially if the rooms are pretty much sealed from other areas of the house, and those other areas aren't leaky themselves. lower pressure means lower resistance through the supply ducts to the "return" rooms, and so you end up with a kind-of a cycle that somewhat bypasses the rooms that aren't line of sight to the return.

in other words, you can have sections of your distribution system that are blowing air into closed spaces like trying to blow into a full balloon, and other open sections that are like blowing air into a toilet paper tube. the tube sections get more wind.

the fresh air return is somewhere near the suction side of the system, or it'd probably be more like a stale air exhaust. i think fresh air returns are built with a high enough constraint to air flow that they don't make a large difference to the (already small) pressure differentials throughout the house (they rely on the suction of the return). i don't know what the code specifically says, but i seem to remember it's something like 10% fresh air.

side question: when they installed the fresh air return, did they put any kind of separate filter on the return, maybe on the outside, or do you just rely on the main intake filter for everything? my neighbor burns something in his fireplace that sticks to the ground and would ruin our house air if we had much of a fresh air inlet, let alone 10%, filtered or not.


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

Thanks for the explanation.

All of the return air (fresh and inside) runs through 5" media filters located just before the furnace. I have to change the filters about once every 5 months or so.

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

1 edit

reply to jig
OK, I think I understand what you're saying here. Unfortunately, the rooms that are having problems are on a hallway with one of the air returns, so those rooms _should_ be getting the good, easy airflow if that was the problem. But they're not.

Thanks,

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."


emptywig
Huh? What?
Premium
join:2002-08-05
Pasadena, TX

reply to SandShark
Sandshark, what were you seeing in my photos that let you know I had a two-stage coil? What would look different on, um...a not-two-stage coil?

wig
--
"There is nothing- absolutely nothing- half so much worth doing as simply messing about in boats."



Ken
Premium,MVM
join:2003-06-16
Brownsburg, IN

said by emptywig:

Sandshark, what were you seeing in my photos that let you know I had a two-stage coil? What would look different on, um...a not-two-stage coil?

wig
I'm guessing that it is because you have 4 lines to the coil instead of 2.
--