  tp0d yabbazooie Premium join:2001-02-13 Carnegie, PA clubs:
·Verizon FIOS
1 edit | reply to Pathfinder Re: Does verizon need to ground fiber?
said by Pathfinder :Most codes require ground wire to be at least 10 guage. Just checked again, says 12 awg on jacket, I was wrong...
I also checked out the NEC 2008.. they specify a minimum of 14awg for fiber and comms circuits. Since the input voltage and current is relatively low, I would think a #12 or 14 would be sufficient..
nec2008 quoted above... 770.100.A.3 on the first pic, and 800.100.A.3 on the 2nd
-j
-- if it aint broke, tweak it!! currently on FiOS (kick aZZ!) |
|
 bogey780
join:2004-03-19 Here | It's not the service voltage. It's foreign voltage (lightning and utility). The gauge usually allows only a certain amount of protection. Meaning the more services protected the higher the gauge needed. 10ga is the way to go. |
|
  tp0d yabbazooie Premium join:2001-02-13 Carnegie, PA clubs: 1 edit | yea, #10 to the ground rod at min... I have #6 here from the main box to the rod, vz just put a bug on it for the fios with #12
so the nec code is wrong?
-j |
|
  NOCMan Verizon Fios User Premium join:2004-09-30 Flower Mound, TX
| reply to bogey780 Grounding is not to protect from being hit by lightning. It's to dissipate the static that could attract lightning and give a low resistance path in case of a electrical short.
I learned that building a home weather station when I had to put the mast up I checked what was needed for lightning protection. |
|
 bogey780
join:2004-03-19 Here | Fiber may be different from POTS but all telephone interfaces have carbon or gas tubes in there specifically with lightning protection in mind. The ground is definitely there in those for lightning. |
|