 NOCManMacChatterPremium join:2004-09-30 Colorado Springs, CO | reply to ThrowDemsOut
Re: Only fixing problem in NY? I looked at this and by NYC's standards my fios box is grounded wrong. They ran it to a clip that's attached to the power box.
I'm not going to bother getting them out here though. I'll run a new wire out to the grounding rod. |
|
 whizkid3Premium,MVM join:2002-02-21 Queens, NY kudos:6 | said by NOCMan:I'm not going to bother getting them out here though. I'll run a new wire out to the grounding rod. That would be wrong too, unless you are planning on bonding the new ground rod. (With much larger wire to the home's existing grounding electrode system.) |
|
 PathfinderDazed ConfusedPremium join:2000-03-26 Mount Vernon, NY Reviews:
·RoadRunner Cable
·Verizon Online DSL
| reply to NOCMan said by NOCMan:I looked at this and by NYC's standards my fios box is grounded wrong. They ran it to a clip that's attached to the power box. I'm not going to bother getting them out here though. I'll run a new wire out to the grounding rod. It's hard to tell from your description. There is a clamp made to go on the side of the Meter box. This is acceptable. However if you mean the breaker panel then no, that is not acceptable, |
|
|
|