Re: X10 Appliance Module: Window A/C???

I just read something about how sensitive the X10 modules are to noise on the AC line, and over/under-volt conditions. I have a huge post (although old) in the electronics forums that chronicals BGE trying to fix poor continuity on my neutral in my house.

When I switch on something with a high inrush current (attic fan), the leg with the fan drops its voltage to ~103VAC, and the other leg runs up to ~130VAC. With a condition like this, I don't think X10 is going to work very well.

EDIT: here's my post on my neutral problem: »Lights dim/brighten during inrush current...

bkjohnson
Premium
join:2002-05-22
Birmingham, AL

reply to i1me2ao
When I Googled window AC remote T saw a 5000 BTU model with a remote for $120 at Walmart. I didn't read the particulars. It seems to have a timer function. Here's a link.
»www.walmart.com/catalog/product.···10998012
There were lots of other links.


i1me2ao
Premium
join:2001-03-03
TEXAS
reply to bkjohnson
do they have a small 5000 btu a/c that can run from say 12 pm till 9 pm daily?

bkjohnson
Premium
join:2002-05-22
Birmingham, AL
reply to batsona
Any chance that you could replace the A/C with one that comes with a remote as part of the unit? Several companies seem to make them.


i1me2ao
Premium
join:2001-03-03
TEXAS
·Comcast

reply to batsona
dont loose sleep over it. they will fight just to fight. we just got back from mom and dads and they refuse to ride next to each other in van cause they had to sleep in same bed for three days.
--
calling a illegal alien undocumented is like calling a drug dealer a undocumented pharmacist


cowboyro

join:2000-10-11
Shelton, CT
·AT&T U-Verse
·Comcast
·Optimum Voice

reply to batsona
said by batsona See Profile :

When I was able to run the modules years ago when I had HomeSeer installed, I remember the Appliance Modules made a loud *bang* when the relay would close the switch inside, so I'd say it's a mechanical contactor in there...
The 40W min load of this particular module is a good hint that it uses a solid state device.

batsona
Maryland

join:2004-04-17
Ellicott City, MD
reply to cowboyro
When I was able to run the modules years ago when I had HomeSeer installed, I remember the Appliance Modules made a loud *bang* when the relay would close the switch inside, so I'd say it's a mechanical contactor in there...

Waterbug

join:2008-03-30

reply to Raphion
Incandescent bulbs ??? Are they still legal ??? Aren't they a MAJOR contributor to Global Warming ? Every time someone turns on an incandescent bulb, it probably kills a Polar Bear.

Sorry, I just couldn't resist. Won't be able to get my tongue out of my cheek for a week.


royphil345
Premium
join:2004-12-10
Lakewood, OH
clubs:


1 edit
reply to DrD
said by DrD See Profile :

Uphill both ways, of course!
... and high as a kite!... lol

bemis

join:2008-07-18
Stoneham, MA
·Sprint Mobile Broa..
·Verizon FIOS
·Comcast
·RCN CABLE

reply to nunya
said by nunya See Profile :

You are correct, it's a non-issue.
Unless we're talking about X10 modules!! :-D


cowboyro

join:2000-10-11
Shelton, CT
·AT&T U-Verse
·Comcast
·Optimum Voice

reply to bemis
said by bemis See Profile :

I wish I had paid more attention in school... because what you said does not seem right.

It does not take 12A to start a 100W light bulb..... does it?

My living room has 5 100W bulbs on a single switch, so does that mean it draws 60A when I flip the switch to on?

I suppose it might be believable if the current draw is nearly instantaneous and so it occurs so quickly that there is no time for the fuses/circuit breakers to blow or the wiring to heat up...
Yes, the instant start current can be very high, but it's only for a fraction of a second. It could be up to ~17A/bulb (on the peak of the sine wave) if the resistance of the filament is 10ohm when cold. But it only lasts for a very, very short time. Even if it starts with the 17*5=85A, 8ms later it will be 0...
Haven't you noticed that bulbs tend to burn when you switch them on?


nunya
SEE ROCK CITY 475 MILES
Premium,MVM
join:2000-12-23
O Fallon, MO
clubs:
·AT&T CallVantage

reply to batsona

I suppose it might be believable if the current draw is nearly instantaneous and so it occurs so quickly that there is no time for the fuses/circuit breakers to blow or the wiring to heat up...


You are correct, it's a non-issue.
--
Looks like Reverend Wright got his wish - God Damn America.

bemis

join:2008-07-18
Stoneham, MA
·Sprint Mobile Broa..
·Verizon FIOS
·Comcast
·RCN CABLE

reply to Raphion
said by Raphion See Profile :

I just checked the resistance of a 100 Watt incandescent bulb; it's 10 ohms, and 10 ohms at 120 volts is 120/10= 12 Amps! Surprising how much of a jolt those bulbs take to start up eh? It's an extremely short spike of current before the filament gets hot, but it still needs to be considered, especially with devices that use solid state electronic switches.
I wish I had paid more attention in school... because what you said does not seem right.

It does not take 12A to start a 100W light bulb..... does it?

My living room has 5 100W bulbs on a single switch, so does that mean it draws 60A when I flip the switch to on?

I suppose it might be believable if the current draw is nearly instantaneous and so it occurs so quickly that there is no time for the fuses/circuit breakers to blow or the wiring to heat up...


cowboyro

join:2000-10-11
Shelton, CT
reply to batsona
The real stress will be starting the compressor, not running it. Honestly I don't see the control device (solid state relay, triac, thyristor) lasting too long - but you may as well be lucky.

batsona
Maryland

join:2004-04-17
Ellicott City, MD
·Verizon FIOS
·Vonage

reply to batsona
UPDATE: I took the A/C unit (6000BTU Whirlpool unit from early '90s) and ran the compressor constantly for 45 min. I was pleased to see that the front of the Appliance Module got slightly warm, but then leveled off (didn't keep getting warmer and warmer..) I guess I can feel safe that the unit won't melt.

Raphion

join:2000-10-14
Samsara

reply to TheMG
said by TheMG See Profile :

said by nunya See Profile :

Yeah, considering an incandescent load is purely resistive (for all intents and purposes).
Actually, there might yet be some logic behind that spec.

Incandescent bulbs have a very high inrush current when first turned on, which that X10 device may not be able to handle beyond 15A of inrush current. Something like that anyways.
Bingo, incandescent bulbs have HUGE inrush current, because the resistance of the filament is proportional to it's temperature. So when it comes on, it's cold and low resistance, and draws a surge of current till it gets hot.

I just checked the resistance of a 100 Watt incandescent bulb; it's 10 ohms, and 10 ohms at 120 volts is 120/10= 12 Amps! Surprising how much of a jolt those bulbs take to start up eh? It's an extremely short spike of current before the filament gets hot, but it still needs to be considered, especially with devices that use solid state electronic switches.

DrD

join:2008-03-03
Harrisonville, MO
reply to SparkChaser
Uphill both ways, of course!

batsona
Maryland

join:2004-04-17
Ellicott City, MD
·Verizon FIOS
·Vonage

reply to SparkChaser
Not to hijack my own thread, but my kids started to try to kill each other (9, 11) so we put them in seperte rooms. I'm an only child, and my mother is too -- I can't figure out why siblings fight.. Anyway.. I'll buy my $49 copy of ActiveHome with the Macros, and see if the Appliance module melts. The TStats in the A/C units routes the full current of the compressor thru it - I thought it might be a low voltage relay, then I could have controled it as a 24v relay, but no such luck.


SparkChaser
BURY BECK
Premium
join:2000-06-06
Downingtown, PA
·Verizon FIOS
·Comcast

reply to nunya
said by nunya See Profile :

A proper solution is to install a dedicated circuit for each window unit. For all the confabulation and speculation with X10 stuff, you could devote that time, energy, and funding to correcting the original problem.
I was thinking the kids could bunk together and alternate rooms

Did I tell ya, how we didn't have A/C and I walked 10 miles to school in the snow?
--
"Facts do not cease to exist because they are ignored." - Aldous Huxley

"I'm tellin' you, man, every third blink is slower" - Fillmore



nunya
SEE ROCK CITY 475 MILES
Premium,MVM
join:2000-12-23
O Fallon, MO
clubs:
·AT&T CallVantage

reply to batsona
A proper solution is to install a dedicated circuit for each window unit. For all the confabulation and speculation with X10 stuff, you could devote that time, energy, and funding to correcting the original problem.
--
Looks like Reverend Wright got his wish - God Damn America.
Forums » Tech and Talk » Technical » Home Repair & ImprovementRe: plugged toilet »
« wasp problemb  
page: 1 · 2


Wednesday, 09-Dec 07:00:45 Terms of Use | Privacy Policy | Hosting by www.nac.net - DSL,Hosting & Co-lo | feedback | contact
over 10 years online! © 1999-2009 dslreports.com.
page compression OFF
Most commented news this week
· [194] Sprint Sued For Distracted Driving Death
· [81] 3G Network Test Says AT&T Is Tops
· [72] Mediacom Unveils 105 Mbps Pricing
· [62] Sprint Poised For A Turnaround?
· [51] WPA Cracker: Test WPA-PSK Networks In 20 Minutes
· [50] The Future Of Wi-Fi Is Bright
· [47] Site Leaks Yahoo, Verizon Fed Data Share Pricing
· [44] Microwaving Your Innards Is Not 'Extreme'
· [39] Verizon LTE: 5-12 Mbps Downstream
· [21] AT&T Releases Network Reporting iPhone App
Most people now reading
· Windows 7 boot manager editing questions [Microsoft Help]
· Comcast refused to install 400' feet. [Comcast HSI]
· [How to] Install Asterisk on an Asus WL-520GU router [VOIP Tech Chat]
· persistent connection to qw-in-f113.1e100.net on boot [Security]
· Tomato/MLPPP v3 alpha 6 released! [TekSavvy]
· Maximizing Rogue DPS for 3.1 [World of Warcraft]
· Extjs grid combo box. [Webmasters and Developers]
· Errrybody must be stuck home from the snow [Mediacom]
· CRTC Response to ME: You will be Band F FOREVER!!! [TekSavvy]
· Servers UP!!! [World of Warcraft]