republican-creole
Search:  

 
 
   All ForumsHot TopicsGallery






how-to block ads


 
Forums » O Canada! » Canadian » TekSavvy » TekSavvy Down (EDIT: Now back online)
Search Topic:
Uniqs:
6157
Share Topic:
RSS topic:
toggle:
flat / full
normal / watch
Posting:
Post a:
Post a:
A cowboy and the Government »
« Problems with IRC  
page: 1 · 2 · 3 · 4 · 5 · 6 · 7
AuthorAll Replies

Davesnothere

join:2009-06-15

reply to Guspaz
Battery Types

It's my understanding that they are a variant of Lead-Acid called a 'Gel Cell' battery and are supposed to be completely 'maintenance free' (cannot top up the electrolyte as it is not a free flowing liquid), unlike some lead-acid car batteries which were also known as 'maintenance free', though Could be topped up if you pried off some covers believing you needed to.

Those car batteries are now are called 'Low Maintenance', due to changes in / enforcement of consumer laws, I believe.


jfmezei
Premium
join:2007-01-03
Beaconsfield, QC
·ELECTRONICBOX


1 edit
Many moons/centuries ago, I visited the Bell CO on Belmont street in Montreal. They still have crossbar equipment feeding McGill university back then. (this was one step ahead from the first generation rotary switches, and the first to support touch tone). And they still had one rack of rotary (step by step) switches, but they had just been made offline and not yet removed).

They had a large portion of a floor dedicated to batteries. They had semi transparent plastic enclosure, and you could see bubbles flowing up between the metal plates inside. Pretty neat sight.

When I worked for a bank, I did see their turbine generators on the top floor, but I don't recall their batteries. (that would have been about 10 years after visiting the Belmont one). When I visited the Whitehorse CO in 1989 they had more modern equipment there. (and got to meet some of the operators, some of whome I spoke t later on when making calling card calls


Guspaz
Guspaz
Premium,MVM
join:2001-11-05
Montreal, QC
reply to TSI Marc
Re: TekSavvy Down (EDIT: Now back online)

Consumer/business UPS are technically "sealed" lead-acid batteries that don't need to be run in any given orientation (as in they run fine upright or on their side). I'm not sure if they're gel-based or not.


Thane_Bitter

join:2005-01-20
London, ON
·Bell Sympatico

reply to EG
Re: TekSavvy Down

It could happen, here is an example of a battery issue in a APC smartUPS UPS (I think it’s the 2200 model, the pic looks identical to one I have...minus the damage ). The right most battery has broken internally (short, overcharged, or just plain broke) and had been generating gas for some time. SLA batteries do have a vent valve that is designed to release the excess gas; however nothing is 100% reliable. It failed as well and the preasure built up over time causing the cell to swell up. Assuming the rest of the UPS is unaffected you have to disconnect everything and remove the top cover do remove swollen batteries (a rackmount UPS with batteries in it is a very heavy thing to move).
»farm3.static.flickr.com/2291/226···f4_b.jpg

Davesnothere

join:2009-06-15
Interesting.

I have encountered some smaller APC's where the battery had swelled to the point that it had to be Pried out.

HeadSpinning

join:2005-05-29
Windsor, ON

said by Davesnothere See Profile :

Interesting.

I have encountered some smaller APC's where the battery had swelled to the point that it had to be Pried out.
Pregnant batteries in APC UPSs is a common problem.

I had always supsected they're running the float voltage too high. A few years ago, I was at a lunch seminar and was seated at a table with one of the founders of APC, and he basically confirmed (without actually saying it...) that some units have a problem with float voltage regulation, that might cause battery failure.


An_Onymous

@teksavvy.com

reply to TSI Marc
Re: TekSavvy Down (EDIT: Now back online)

The original article reference from slashdot's headline:

»www.datacenterknowledge.com/arch···-uptime/

- power outage at its Dallas data center
- Early Thursday Equinix Inc. (EQIX) data centers in Sydney, Australia and Paris each experienced power failures.
- Google App Engine, the company’s cloud computing platform, had lengthy performance problems on Thursday, experiencing high latency and data loss.
- A fire at Fisher Plaza in Seattle late Thursday night left many of the building’s data centers without power.
- Early Sunday, July 5, a fire at 151 Front Street, the major carrier hotel in Toronto, knocked out power on several floors of the facility used by Peer 1 networks.


Inssomniak
Premium
join:2005-04-06
Cayuga, ON

reply to TSI Marc
Click for full size
At least it was early.


DKS
Damn Kidney Stones
Premium,ExMod 2002
join:2001-03-22
Owen Sound, ON
clubs:
·Bell Sympatico

reply to TSI Marc
Peer 1's official response:

From: "Ted Smith"
Date: July 7, 2009 6:04:33 PM GMT-04:00
To:
Cc: "'Dorothy Williams'"
Subject: Toronto Data Center -- 151 Front Street Post Mortem

Dear Valued Customer,

As you are aware, over the weekend the 8th floor of PEER 1’s Toronto data center located at 151 Front Street experienced a fire with a UPS cabinet that set off a chain of events that resulted in power outages in multiple suites and network outages in others. I have detailed the events below.

PEER 1 is extremely thankful that no one was injured during the fire. The fire itself was contained within a single UPS cabinet and the Toronto fire department was able to extinguish it with the use of dry chemicals. No water was used, which significantly reduced the damage and aided in our ability to restore services to all data centers as quickly as possible.

I was personally involved in PEER 1’s response to the situation, and would like to take a moment to apologize to you for the information contained within our first few email alerts regarding the outage. When we were first organizing the team, we received an early report from our on-site staff that all power was out at 151 Front Street. That was not accurate. The fire caused a power outage in PEER 1’s suite 802. The local fire department cut power to PEER 1’s suite 709 as a preventative and safety measure to contain and extinguish the fire. The network gear providing connectivity for Suite 816 are kept in a cage in Suite 802. As a result, Suite 816 suffered a network outage. Power in the rest of the building was unaffected throughout the incident. There is a fine balance to providing information during a crisis, and we do our best to make sure updates to our customers are, quick, transparent, and accurate. In no way would we try to misrepresent the situation.

PEER 1 manages all of the equipment it provides to customers with safety and performance in mind. The UPS mentioned above has been in service for approximately four years. Its last service inspection was on July 2nd and it was only at 65% load. We do not yet have the root cause, but there was nothing in the unit’s maintenance record to indicate there was potential for a problem. Our service contractor and manufacturer are both involved in the investigation.

As part of the process to restore power quickly, we had to bypass the affected UPS. This means that suite 802 is running without UPS power until we can schedule delivery and replacement. We will expedite the process and keep customers in this suite up-to-date with the latest information on the timeline.

Outage Details:
(Timelines represent impact to “most” clients. Some specific network devices failed due to power loss and restore took longer.)
· Suite 802 – Power and network outage. Start 23:32PT End 03:10PT
· Suite 816 – Network outage. Start 23:32PT End 03:10PT
· Suite 709 – Power and network outage. Start 23:32PT End 00:50PT
· Suite 402 – Limited network outage (some latency/packet loss issues). Start 23:32PT End 00:50PT
· Firewall Clients. Network outage. Start 23:32PT End 03:10PT

Ted Smith
SVP, Operations

PEER 1
1000-555 West Hastings Street
Vancouver, BC, Canada V6B 4N5
tsmith@peer1.com
T: (678)365-2896
F: (678)365-2956
www.peer1.com
--
Need-based health care not greed-based health care.

LazMan

join:2003-03-26
Angus, ON
·TekSavvy Solutions..

reply to Guspaz
said by Guspaz See Profile :

Consumer/business UPS are technically "sealed" lead-acid batteries that don't need to be run in any given orientation (as in they run fine upright or on their side). I'm not sure if they're gel-based or not.
"Gel-Cell" is a misnomer... VRLA's (Valve regulated lead acid) batteries do use a liquid electrolyte (aka acid) but it's absorbed in fibreglass mats between the lead plates. A large VRLA will only have about 2 cups of liquid within it, unlike "flooded" cells that may have gallons.

Headspinning - not only do I remember 220 Simcoe - I was there... Bell's union wouldn't let their people in - Nortel's had no such issue - so in we went, to try and bring equipment back online.


51019512

join:2009-05-19
151 Front St
reply to Inssomniak
said by Inssomniak See Profile :

At least it was early.
What program is that?
-
Forums » O Canada! » Canadian » TekSavvyA cowboy and the Government »
« Problems with IRC  
page: 1 · 2 · 3 · 4 · 5 · 6 · 7


Thursday, 26-Nov 14:07:03 Terms of Use | Privacy Policy | Hosting by www.nac.net - DSL,Hosting & Co-lo | feedback | contact
over 10 years online! © 1999-2009 dslreports.com.
page compression OFF
Most commented news this week
· [108] New AT&T Ad Campaign Hits Back At Verizon
· [105] Time Warner Cable Fires Broadside At Broadcasters
· [95] Apple Joins AT&T Verizon Snark Fest
· [87] New Bill Takes Aim At Higher Verizon ETFs
· [69] TiVo Sees Record Customer Losses
· [57] In-Flight Internet Headed For Bumpy Landing?
· [35] ICANN Slams DNS Redirection
· [34] Senators Want ACTA Made Public
· [33] Despite Billions In USF Fees, U.S. Libraries Lack Bandwidth
· [30] Earthlink Suffers From Major E-mail Outage
Most people now reading
· I'll Just Unplug That... [No, I Will Not Fix Your #@$!! Computer]
· Windows 7 boot manager editing questions [Microsoft Help]
· 3.x Feral Druid - Bear Tanking Guide [World of Warcraft]
· Newegg Black Friday Sale started [Users Find Hot Deals]
· Connecting to Google Voice Via SIP [VOIP Tech Chat]
· Slow speeds in the evenings [TekSavvy]
· What is the spell hit cap for a lvl 80 full arcane spec mage [World of Warcraft]
· HOW-TO: QoS and Tomato (fixes "choppy voice") [MagicJack]
· 14 Days left [TekSavvy]
· Ottawa South Highspeed - WOW! [Canadian Broadband]