Electical Sub panel

I have a detached garage with a one inch conduit runing in between. The whole garge is running off one 15 amp circuit in my basement. So when it flips i have to go inside and flip it back on. I want the breaker in the garage. I decided to put in a sub panel. It would only be 50 amps. I am going to run 6 awg to the sub pannel. I want to do pretty much what is diplayed here »www.hammerzone.com/archives/elec···view.htm

Can i fit 3 6 awg thhn wires plus a ground in the conduit?

Can I use the conduit as the ground?

If I use thhn what size ground wire should i use?

Would it be better/easyer if I run 6/3g romex in the pipe?

Is it 50 amps total between the 2 feeds or 50 amps per feed?


dgilbert
Good Bye My Friend
Premium,MVM
join:2002-06-15
none
clubs:

1" will handle 4 #6 or 3 #6 an 1 #8 for ground. you may or may not need additional ground rods, i'll leave that to others.

i dunno about using the conduit for ground, so i will leave that to others.

you can't use "romex, it would have to be UF just like if you use individual wires they must be THWN. the conduit will be considered a wet location so the conductors must be wet rated.

50A at 240V.

BTW, how long of a run will it be? if under 100' #6 is ok for 50A, but over you need to go up to #4 for the conductors and at least #6 for ground. the ground cna be 1 size smaller than the conductors.
--
Lack of Preparation on YOUR Part does NOT Constitute an Emergency on Mine!

Msradell

join:2008-12-25
Louisville, KY
Filling in a couple of the blanks.

That handle it cannot be used as the ground!

A ground rod is not required at the garage end but also is not prohibited.


nunya
SEE ROCK CITY 475 MILES
Premium,MVM
join:2000-12-23
O Fallon, MO
clubs:
·AT&T CallVantage

reply to ComTech 4
If the conduit is EMT, RMC, or IMC from end to end, and certain fittings are used, you can use it as the equipment ground. However, it's probably cheaper and easier to pull a ground.
#8 copper is your ground wire size.
I highly suggest not trying to jam 6/3 romex down the pipe. It's going to be pretty tight with THHN.

gregz

join:2009-10-01
reply to ComTech 4
The following is what you need to know about hooking up the sub »www.dropshots.com/stubbie4#album···llations


wilbilt
Pronto Resurrected
Premium
join:2004-01-11
Oroville, CA
reply to ComTech 4
I just pulled 4 #6 THHN in 1 1/4" sch40 PVC about 40 feet with 1 90 and 3 45's. It was an easy pull.

1" should certainly be do-able.
--
We were taking a vote when the ground came up and hit us.


Splitpair
Premium
join:2000-07-29
Cow Towne
·T-Mobile US


1 edit
reply to ComTech 4
said by ComTech 4 See Profile :

Can i fit 3 6 awg thhn wires plus a ground in the conduit?
Yes.

Can I use the conduit as the ground?
Yes as Nunya pointed out, however if you did not run the conduit or do not know the condition of the connectors used then run a ground wire as well.

Is it 50 amps total between the 2 feeds or 50 amps per feed?
50 amps per feed hot to neutral at 120 volts or 50 amps hot to hot at 240 volts.

By the way with 1 inch and a little snake snot (wire lube) that will be an easy pull, just be sure to have a helper on hand to feed the wire into the conduit to prevent any damage to the insulation.

Wayne

Wayne
--
If you cannot fix it with a buttset and some beanies you're not a technician.


drjim
Premium,MVM
join:2000-06-13
Torrance, CA
clubs:
"Snake Snot"?
Where I come from, we call it "Gorilla Snot", son!
--
One man's Magic is another man's Engineering.


nunya
SEE ROCK CITY 475 MILES
Premium,MVM
join:2000-12-23
O Fallon, MO
clubs:
reply to ComTech 4
I can't post what we call it.

SuperWISP

join:2007-04-17
Laramie, WY

reply to ComTech 4
Yes, you can fit those conductors in a 1" conduit. But why skimp? Go for something a little larger: 1 1/4" or 1 1/2". Use PVC, not metal, and put in a real ground conductor that's the same size as the other conductors. If you're going a long way, or if you have power tools that contain large induction motors, bump the size of all of the conductors up a notch or you'll dim the lights in the garage due to the voltage drop every time you start up one of those tools. Consider, also, the possibility of driving a ground rod at the garage end and bonding it to the ground bus in the panel with #4 copper; it may help if you get surges due to lightning. Also remember to bond the ground bus to the plumbing, if there is any, as close as possible to where it enters the building.

Remember to remove the jumper between ground and neutral in the subpanel, because there should be only one connection between ground and neutral and it should be back at the main panel.


cdru
Go Colts
Premium,MVM
join:2003-05-14
Fort Wayne, IN

said by SuperWISP See Profile :

Yes, you can fit those conductors in a 1" conduit. But why skimp? Go for something a little larger: 1 1/4" or 1 1/2". Use PVC, not metal
MY guess is that he has an existing run of conduit and would like to reuse it instead of having to dig his own trench and run new.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
·CenturyLink

reply to ComTech 4
There is an error shown here.

You -NEVER- terminate to the CB in the main panel before you terminate the load (shown here as a subpanel). That is asking for trouble. Someone could come along and turn on the CB while you are working on the other end.

Terminate the load, THEN terminate to the source.

Be safe!
--
The man who speaks to you of sacrifice is speaking of slaves and masters, and intends to be the master.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
·CenturyLink

reply to ComTech 4
Also, a "main disconnect" CB might be required by your locality in addition to the CBs feeding your branch circuits in your garage.
--
The man who speaks to you of sacrifice is speaking of slaves and masters, and intends to be the master.

ImpetusEra

join:2004-05-19
00000

reply to ComTech 4
I don't recall exactly what the specifics of the code are but you should at the least find out what your area goes by and follow that. Personally I'd size my wire based on voltage drop for distance and at the garage terminate to a disconnect or main disconnect breaker in the sub panel. For wire I'd run 4, two hots, a neutral and a ground and then drive two 8' ground rods spaced 8' apart at the garage. Either the rods or the ground wire in conduit are a requirement if other metallic paths exist between the building (phone/tv/ethernet/water pipe). I think the rods are required regardless though on account of potential lightning strikes (would go through the rod(s) at the garage instead of following back to the main panel in the house).


Killa200
Premium
join:2005-12-02
Spring City, TN
reply to ComTech 4
If you use rods at the garage, remember the ground you run in the conduit has to be at least a minimum of a #6,


ComTech 4
Premium
join:2002-11-28
USA
reply to ComTech 4
Yes the conduit is existing. Im not going to tare up my concreet driveway to replace it. The total distance of wire would be 30'.
-
Forums » Tech and Talk » Technical » Home Repair & Improvementinstalling foil faced polyisocyanurate foam »
« Drainage issue with pier and beam.  


Monday, 30-Nov 05:15:51 Terms of Use | Privacy Policy | Hosting by www.nac.net - DSL,Hosting & Co-lo | feedback | contact
over 10 years online! © 1999-2009 dslreports.com.republican-creole
page compression OFF
Most commented news this week
· [124] Time Warner Cable Fires Broadside At Broadcasters
· [112] New AT&T Ad Campaign Hits Back At Verizon
· [96] Apple Joins AT&T Verizon Snark Fest
· [87] New Bill Takes Aim At Higher Verizon ETFs
· [82] Weekend Open Thread
· [80] TiVo Sees Record Customer Losses
· [79] Verizon CEO: Hulu Will Be Dead Soon
· [69] In-Flight Internet Headed For Bumpy Landing?
· [63] Thanksgiving Open Thread
· [41] ICANN Slams DNS Redirection
Most people now reading
· Are GPS's better today? [General Questions]
· Is Easynews down? [Filesharing Software]
· [Newsgroups] Newzleech down? [Filesharing Software]
· [How to] Install Asterisk on an Asus WL-520GU router [VOIP Tech Chat]
· Windows 7 boot manager editing questions [Microsoft Help]
· Grey Cup on the Web? [Canadian Chat]
· persistent connection to qw-in-f113.1e100.net on boot [Security]
· [ PVP] 3.2 DK PvP D/W Spec... [World of Warcraft]
· [Snow Leopard] NFS Mounts - no more Directory Utility [All Things Macintosh]
· Considering Leaving Vonage, who should I Consider? [VOIP Tech Chat]