jack bGone Fishing MVM join:2000-09-08 Cape Cod |
jack b
MVM
2009-Dec-27 10:18 am
Outdoor Meter SocketI had my POCO out last night, my lights have been flickering for a while. He opened up the meter pan, and it looks like one of the lower (load) jaws overheated and melted the meter plastic backing around the meter blade. The jaw is also discolored from the heat. I want to find out if the meter itself failed or the socket jaw is in fact bad. As a temporary measure, they jumped the good leg in the socket and I backfed the "dead" leg in my panel by jumpering an unused two pole 50 amp breaker.
In any event, what can I expect to pay for an electrician to replace a 200 amp 240v 2 wire outdoor socket? |
|
|
Savant Premium Member join:2001-08-12 Toronto |
Savant
Premium Member
2009-Dec-27 11:11 am
It would be helpful to see a picture. There are some variables that come into play as to whether they can just swap out the meter box, or whether they have to replace other things as well. (Without getting into particulars, things need to be brought up to code, so a much older install may need to have more done than a newer one.)
I'd tend to lean toward the jaw being loose (if it is an old socket) or perhaps the lug that holds the wire connected to the jaw being loose. (which could also cause a problem) I replaced a meter socket once that had a similar problem and it was because it was missing the small secondary spring clip on the outside of the jaw, and it looked to have been a factory defect.
A straight meter socket swap on a service fed from underground lines shouldn't be more than a couple hours time + materials. The price goes up if things are more complicated. (rigid steel pipe on an old mast that is threaded directly into the socket will require more work to get the old socket out etc.) This is where pictures help. |
|
nunyaLXI 483 MVM join:2000-12-23 O Fallon, MO ·Charter
|
to jack b
Is it overhead or underground? A standard 200A underground situation: I'd probably charge you $209.36. There would have to be enough slack wire left on the feeders.
If it was a standard 200A overhead: $301.77. There would have to be enough slack wire left on the feeders.
If it was a common base, I'd probably pull the guts and just replace those: Probably about $140.00.
This would be on typical installations where all portions are readily accessible. |
|
nunya |
to jack b
All the "movement" is in the jaw. Unless it's a "very smart" (not just "smart") meter, the meter bus is just two chunks of metal wrapped in windings for the meter. If it has been arcing for a while, the meter ear *could* have thin spots on it. I'd have your electrician look at it while it's out. 95% of the time it is strictly the jaw.
Note that the power company will have to come back and cut the power while the meter is being fixed. Anybody that does otherwise isn't qualified to be working on the meter base. |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod |
jack b
MVM
2009-Dec-27 12:45 pm
Thanks! It's an overhead service, no steel mast just service entrance cable in and out. I'll get a few pic's once it stops raining here, and I can sneak away from company visiting. |
|
jack b 1 edit |
jack b
MVM
2009-Dec-27 3:28 pm
It's obvious there was a contact issue with the load cable lug connection, the conductor shows no evidence of CU/AL ever being applied. It looks like somebody did a nasty job trying to repair a water condition. This is an early '70's-vintage install. |
|
scooper join:2000-07-11 Kansas City, KS |
to jack b
All I got to say is "glad it's you and not me having to deal with this". Best of luck and get it fixed right... |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod |
jack b
MVM
2009-Dec-27 4:48 pm
LOL thanks. I forgot the meter pic: |
|
nunyaLXI 483 MVM join:2000-12-23 O Fallon, MO ·Charter
|
to jack b
The silicone just added $75.00 to the job. Good grief! Who did that?
That base is probably "uneconomical to repair", and should be put out of it's misery. Many places do not allow SEU cable to be exposed like that. It appears that there are some water and cable support issues. I'd consider rebuilding the service with conduit, or at the very least new fittings.
My guess is water is entering the cable at the weather head or that crummy fitting on top of the meter. Water, coupled with the fact that there is not any oxide inhibitor on the AL connections may have lead to the heating of that jaw.
If SEU absolutely must enter topside, it should go through a neoprene pressure fitting.
Personally, I'd spend a little more money than just making it "good enough". I'd go ahead and put everything in EMT or heavywall. Since you muni allows exposed SEU, you might even be able to use PVC. |
|
nunya |
to jack b
No signs of damage on the meter. Make sure the poco greases that puppy before it goes back into the new base. |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod 2 edits |
jack b
MVM
2009-Dec-27 5:00 pm
different shot, showing both meter load blades. The meter was left hanging on the pan, and it filled up with water. I think it's a goner. |
|
nunyaLXI 483 MVM join:2000-12-23 O Fallon, MO |
nunya
MVM
2009-Dec-27 5:57 pm
Oh yeah, I can see it got a little warm too. Good thing you don't have to pay for it. The smart meters can run up to $600.00. |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod |
jack b
MVM
2009-Dec-27 7:02 pm
It didn't sound like they were going to charge me for damage to the meter, the guy said they're "throw-aways". It's not "smart" other than it's solid state w/LCD display and they drive a truck down the street and collect the meter readings. My billing is flat rate 24/7, no peak/off-peak, peak demand, etc. |
|
|
said by jack b:It didn't sound like they were going to charge me for damage to the meter, the guy said they're "throw-aways". It's not "smart" other than it's solid state w/LCD display and they drive a truck down the street and collect the meter readings. My billing is flat rate 24/7, no peak/off-peak, peak demand, etc. It can still be reflashed wirelessly into a smart meter with a smart meter billing tier at any time. |
|
Anonymous_Anonymous Premium Member join:2004-06-21 127.0.0.1 |
said by patcat88:said by jack b:It didn't sound like they were going to charge me for damage to the meter, the guy said they're "throw-aways". It's not "smart" other than it's solid state w/LCD display and they drive a truck down the street and collect the meter readings. My billing is flat rate 24/7, no peak/off-peak, peak demand, etc. It can still be reflashed wirelessly into a smart meter with a smart meter billing tier at any time. SoCal Edison IS so cheap they installed a Brand new analog meter reading 00000 it's all ready at 01000+ i think it maybe spinning way too fast |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod |
jack b
MVM
2009-Dec-28 6:57 pm
I was able to get an electrician over today. I managed to get a couple of shots before my camera memory card filled up. |
|
nunyaLXI 483 MVM join:2000-12-23 O Fallon, MO |
to jack b
That's better. |
|
WYXX join:2009-12-21 Riverside, RI |
to nunya
said by nunya:Note that the power company will have to come back and cut the power while the meter is being fixed. Anybody that does otherwise isn't qualified to be working on the meter base. Unless you're an electrician on This Old House. |
|
dosdoxies Premium Member join:2004-12-15 Wallingford, PA |
to jack b
And I hope you remembered to "unjump" that 50 amp double pole in your panel! |
|
nonymous (banned) join:2003-09-08 Glendale, AZ |
to jack b
That is why I do not use any electrician. All that expensive work. Just pounds some nails in to hang the drop off of. Any old box enclosure you have floating around the house. Then a few wire nuts. All done, unless you want to paint the new drop and box to match the house. The cable is rated for outdoor use so paint will not hurt it. No need for conduit. Plus you have the exposed neutral if you ever need to attach to it for anything. In conduit you would have to cut a hole to get at it. Electricians are just a waste of money. |
|
Nick_L Premium Member join:2003-01-22 Pittsburgh, PA |
to jack b
Off topic: While not my personal taste, I must compliment you on your home. It has a very warm, inviting quality to it. It also appears very well maintained. Nice.
Nick |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod 1 edit |
to dosdoxies
said by dosdoxies:And I hope you remembered to "unjump" that 50 amp double pole in your panel! My electrician said the exact same thing as I was firing up my suicide generator connection. Thank you, Nick. |
|
1 edit |
to nonymous
said by nonymous:Plus you have the exposed neutral if you ever need to attach to it for anything. In conduit you would have to cut a hole to get at it. Electricians are just a waste of money. Remember to connect your lightning rods to the neutral, its all ground right? Why use wirenuts? I prefer tire air caps, or twist with fingers then 99 cent store non-UL electrical tape. Use Tupperware for junction boxes. If your short on wire, use coat hanger wire or razor wire with some roofing tar as insulator, your papa did it in his days, it was called knob and tube. Don't waste time and $ with romex staples, just carefully drive a nail between the neutral and ground, thats why the wires flat. |
|
davidgGood Bye My Friend MVM join:2002-06-15 00000 |
to jack b
around here the jakelegs at the poco would have said the meter base was corroded and then proceeded to plug/unplug the meter several times rapidly to "clean" it. i shit you not, they did that once and hosed a couple of transmitters at one ouf our tower sites. bad thing was my tech was reaching for the disconnect right next to the meter when the guy did it. |
|
drjim MVM join:2000-06-13 Long Beach, CA |
to nunya
nunya....what do they use for "grease"? |
|
OCP Premium Member join:2004-10-11 USA |
OCP to Nick_L
Premium Member
2009-Dec-29 11:42 pm
to Nick_L
Ditto. I hope the repairs only add more value. |
|
MdocEhh... munch munch... what's up, Doc? Premium Member join:2007-03-27 Sterling, VA |
Mdoc
Premium Member
2009-Dec-29 11:47 pm
I would think the repairs only restores value, not add to it. |
|
nunyaLXI 483 MVM join:2000-12-23 O Fallon, MO ·Charter
|
to drjim
Most of them carry ILSCO oxide inhibitor: » www.ilsco.com/ProductsDe ··· uPeME%3D |
|
drjim MVM join:2000-06-13 Long Beach, CA |
drjim
MVM
2009-Dec-30 12:22 am
Ok, that's kinda what I thought they might use. |
|
|
to jack b
I'm curious how your Christmas candles in the window are lighting up when there's no power to the house? |
|