Some network Pron :)

Click for full size
New UPS
Click for full size
Click for full size
Fiber :)
Click for full size
Back of Patch
My office network that it's been build.

We're moving location, and construction is on his way.

That a small part of one of our system room

1st pic: Ups for that room, and some pc in the office. A generator is backing that.

2nd: the rack on the left have phones lines, and for now, a Cisco 3900 router. On the right, the patch panel for 75% of the office (550 ports)

3rd: 2 fiber coming in... one MPLS link and the other a regular internet connection

4rd: back of the patch.. on the top left, the green cable.. 10gb ethernet, to link with the other switch room

More yet to come
--
Rogers - Blackberry Bold 9780
Blackberry Playbook 32gb


Marshal
Premium
join:2003-11-01
Montreal

Click for full size
The Conferences room controller (6 room)
Click for full size
The sweet Cisco stuff!
Click for full size
Cisco Telepresence Screen
Click for full size
The phones :) Cisco 7945
Click for full size
The Core... Catalyst 4506
New update...

themagicone

join:2003-08-13
Minneapolis, MN

reply to Marshal
I want to get into doing work like that SOOO bad. Just got my CCNA, working on CCNA Security right now. Any internships open? Paid or unpaid, I don't care!



jmich
Premium
join:2001-08-28
Toms River, NJ

reply to Marshal
Very nice! Thanks for sharing. Lots o' fiber.



shaboah

@sbcglobal.net

reply to Marshal
Nice equipment, poor provider (cogent).. its too bad really.. good luck



Marshal
Premium
join:2003-11-01
Montreal

said by shaboah :

Nice equipment, poor provider (cogent).. its too bad really.. good luck

We have them as a backup link. But we never had any issue with them.
--
Rogers - Blackberry Bold 9780
Blackberry Playbook 32gb


whizkid3
Premium,MVM
join:2002-02-21
Queens, NY
kudos:8

reply to Marshal
Nice.

What is that 'black box' behind the UPS?



Marshal
Premium
join:2003-11-01
Montreal

said by whizkid3:

Nice.

What is that 'black box' behind the UPS?

Its the breaker panel (200Amps) for the equipment connected on the UPS.
--
Rogers - Blackberry Bold 9780
Blackberry Playbook 32gb


whizkid3
Premium,MVM
join:2002-02-21
Queens, NY
kudos:8

Oddly enough, it doesn't look like a breaker panel. Can you get a better photo of it?

The reason I ask is that the UPS is placed directly in front of the panel. I would bet that Canada's electric code requires 36" of working clearance in front of electrical panels, just like the NEC does. You should ask your electrician. (208V, grounded metal object in front.)

Your network equipment and low-voltage wiring job looks fantastic. I can't say the same about the electrical installation, unfortunately. There are a number of basic code violations.


TheMG
Premium
join:2007-09-04
Canada
kudos:1
Reviews:
·TekSavvy DSL

reply to Marshal

said by Marshal:

said by whizkid3:

Nice.

What is that 'black box' behind the UPS?

Its the breaker panel (200Amps) for the equipment connected on the UPS.

Am I correct if I were to guess that the breaker panel is a special one that provides the ability to externally bypass the UPS?


whizkid3
Premium,MVM
join:2002-02-21
Queens, NY
kudos:8

1 edit

That's what I was thinking - maintenance bypass panel, which normally have breakers. Many have ability to synchronize the UPS output with the bypass, so that they can be transferred to bypass and back, with a closed-cycle transition and not interrupt power. Still needs to have the minimum working clearance. If I had to guess, the photo shows the function of the conduits.

TheMG
Premium
join:2007-09-04
Canada
kudos:1
Reviews:
·TekSavvy DSL

I think I found it (or at least, a similar looking panel):

»www.apc.com/resource/include/tec···FC1M1-WP

That panel is quite big, it's actually 37" wide. Hard to tell for sure from the photo, but I'd say there's probably 36" or more of space behind the UPS if you estimate the proportions.



whizkid3
Premium,MVM
join:2002-02-21
Queens, NY
kudos:8

1 edit

 
Click for full size
said by TheMG:

there's probably 36" or more of space behind the UPS

I would bet there is not; just by looking at the length of conduit after the bend. True, there is some flex that you can't see; but after designing enough of these jobs, and seeing many similar computer rooms; I would say no until I see a photo with the measuring tape. Here are pictures of two similar APC UPS installations - same problem, not meeting working clearance requirements.

Thanks for the link, though. I can say, thank god the OP got a maintenance bypass panel. There is nothing worse than having a UPS whose power to the load must be cut to perform normal maintenance on the UPS system.

TheMG
Premium
join:2007-09-04
Canada
kudos:1
Reviews:
·TekSavvy DSL

said by whizkid3:

There is nothing worse than having a UPS whose power to the load must be cut to perform normal maintenance on the UPS system.

Indeed. I've actually had a situation a few months ago where a UPS at one of our sites kicked the bucket. Power had to be shut down several times during the process of replacing the UPS, which meant lots of after-hours work (which for us is after 22:00) and overtime.

All in all it was a huge PITA.

But, we did have a MBP installed along with the new UPS, so that should never again be an issue.

I'm actually surprised we managed to keep proper clearances to all the panels, considering the size of the room, which I'd say is no bigger than 10'x10', and has the UPS, 4 panels, and a 20kVA transformer.