 | New home build framing question. So they finally started framing. They did the main metal support beam and the joists and the the joist caps.
My first question is on the joist caps. It appears the cap was bowed so they did a series of thin notches so it could be flattened out. Is this allowed or would it cause any issues down the road? It doesnt appear to me that it would mater.
PICS:  
Second question is on the main support beam it doesn't appear that the shims are done correctly. Thoughts?
PIC: |
|
 Zach 58Premium join:2006-11-26 NW Minnesota | Since they are using dimensional lumber for the joists, the kerfs in the band board would probably pass inspection. I wouldn't accept it though; it's poor workmanship. The shim job under the beam is inadequate. Our local inspector would flag it for sure. -- Zach |
|
|
|
 nunyaWho is John Galt?Premium,MVM join:2000-12-23 O Fallon, MO kudos:8 Reviews:
·Charter
·surpasshosting
| reply to rbnice1 Your concerns are legitimate. I'd throw down a red flag until they are addressed. The band board isn't just there to hold the joists up. It serves a lateral purpose as well (think earthquake). I've never seen this done before. If the lumber is shit, you toss it (or cut it for use elsewhere) and get a new piece.
The shims are not acceptable either. They should be steel, and at least the size of the beam plate (and stacked properly!). A lot of builders grout the pocket. Not sure if that's required or not. -- If someone refers to herself / himself as a "guru", they probably aren't. |
|
 | reply to rbnice1 Called the foreman with my concerns. He said kerfs are a normal thing for them but he is going to look at it. I could understand a kerf or 2 in a long run but 4-5 kerfs in a 12 foot segment seems bad.
He also said he will be by tomorrow morning to look at it.
Thanks for the input. I will be posting occasionally as things come up that I am unsure on, and really appreciate the knowledge here! |
|
 Zach 58Premium join:2006-11-26 NW Minnesota | After reading Nunya's post and recalling MO is an area with a good bit of seismic activity, stand your ground on those band boards and beam shimming! What they've done is very far from customary and accepted practice -- Zach |
|
 H_T_R_NPremium join:2011-12-06 Valencia, PA kudos:1 | reply to rbnice1 HELL NO!!!! With as glaring a crap job this early I would be sure to be there every day to check on things. If you cant be there hire some that can. The "shims" would cause me to loose it! |
|
 | I plan on being there almost daily. If I am not my mother will be cause the kids school is across the street.
Luckily the new house is only 10 minutes from the apartment we are renting. |
|
 KenPremium,MVM join:2003-06-16 Markle, IN | reply to rbnice1 The rim joist being cut like that is just pure laziness. If you have a joist that bad, you call up your lumber guy and make him run you out a new one. Those shims under the beam are really half-ass.
Now with that said, everything you have posted is completely inline with your average production framing crew. If you pointed out that rim joist they truly wouldn't understand why you have a problem with it. They will say they do it all the time, and so does everyone else. The sad truth is, they would be right. If you are forced to keep using that framing crew I would be in there every day watching them, putting a level on things, and measuring what they are doing and comparing with the blueprints. |
|
 MsradellP.E.Premium join:2008-12-25 Louisville, KY | reply to rbnice1 That notch they made to clear the anchor bolt is also not acceptable! |
|
 Zach 58Premium join:2006-11-26 NW Minnesota | Not to mention, there appears to be only one anchor bolt in the 12-foot run in the picture. It's looking like the OP has a long, hard road to travel with this crew.  -- Zach |
|
 kherrPremium join:2000-09-04 Collinsville, IL Reviews:
·Charter
| reply to rbnice1 Make sure that when they stud the walls the studs are directly in line with the joists. When in-line the weight on the studs/wall will bear down on the joist. Needs to be done on interior walls also. The drywallers may complain, but your plumber/HVAC people will love it. They will be able to use the whole space between studs to drop their pipes. I always run a bead glue under each wall too, won't move around afterwords, but if it is off the line, it's a bitch to correct. |
|
 | reply to Msradell How should the anchor bolt notch been done? I didn't think there was anything wrong with it.
Also the anchor bolts are spaced pretty evenly I would have to measure but they are like every 3 foot.
Will have to buy a long level all my tools are in a pod storage. And will watch the walls to make sure they are placed over joists and not in between them.
I will also have to see if I can get them to email me a copy of the blueprints.
Thanks again guys! |
|
 BobAccount deleted join:2012-07-22 New Jersey | Isn't this the sort of oversight that the General Contractor should be doing? (Or are you acting as the General Contractor?) |
|
 Coma Thanks StevePremium join:2001-12-30 NirvanaLand | reply to rbnice1 said by rbnice1:How should the anchor bolt notch been done? I didn't think there was anything wrong with it.
Also the anchor bolts are spaced pretty evenly I would have to measure but they are like every 3 foot. Who ever poured the foundation screwed up with the placement of the anchor bolt that needed the notch in the band board.
-- August is National Eye Exam Month |
|
 garys_2kPremium join:2004-05-07 Farmington, MI | reply to rbnice1 I can picture a future split propogating up from that bolt clearance notch (it is a stress concentrator) up to the kerf. At that point the integrity of that whole board is shot. |
|
 wthPremium join:2002-02-20 Iowa City,IA | reply to rbnice1 Is there the possibility that the rim joists were cut because the concrete is not not level, but dips down from the corner? |
|
 MsradellP.E.Premium join:2008-12-25 Louisville, KY Reviews:
·AT&T U-Verse
| reply to rbnice1 said by rbnice1:How should the anchor bolt notch been done? I didn't think there was anything wrong with it.
The anchor bolts should be put inside of the joist caps. They hold the sill plate down. It's obvious that the concrete crew put them in the wrong place. I don't see any other ones that required notching in your pictures, are there? This could become a major problem in the long run. Not only is mentioned by others could lead to the deterioration of the member but it's also a hole in the envelope of the structure that could affect air infiltration if not properly sealed. |
|
 cdruGo ColtsPremium,MVM join:2003-05-14 Fort Wayne, IN kudos:7 | reply to Coma said by Coma:Who ever poured the foundation screwed up with the placement of the anchor bolt that needed the notch in the band board. It's nothing a saws-all, 1/2 masonry bit, threaded rod and some epoxy wouldn't fix. Properly. |
|
 | reply to nunya said by nunya:The shims are not acceptable either. They should be steel, and at least the size of the beam plate (and stacked properly!). A lot of builders grout the pocket. Not sure if that's required or not.
Where I am, the shims are required to be welded to the beam and the pocket grouted. It would also be a good idea to brace the beam laterally with metal welded to it - before grouting.
That's among the poorest installs I've seen. |
|
 | reply to cdru said by cdru:said by Coma:Who ever poured the foundation screwed up with the placement of the anchor bolt that needed the notch in the band board. It's nothing a saws-all, 1/2 masonry bit, threaded rod and some epoxy wouldn't fix. Properly. +1 |
|