Re: Why only 1 ground terminal and 2 hot/neutral on receptacles?

said by Speedy Petey:

Sorry, but this is NOT the "proper" way. It is one way.

What is the "proper" way? Or were you just saying that there is no one "proper" way?

Zach1
Premium
join:2006-11-26
NW Minnesota

1 edit

said by alkizmo:

said by Speedy Petey:

Sorry, but this is NOT the "proper" way. It is one way.

What is the "proper" way? Or were you just saying that there is no one "proper" way?

If the circuit in question is NOT a MWBC, either feeding through the device and pig-tailing is generally acceptable. Some AHJ's require and some ECs prefer to pig-tail. For MWBCs, feeding through the device isn't allowed on the grounded conductors. Obviously, in the case of GFCI receptacles, you have no choice but to feed through if you are also protecting loads down-stream.

Edit to add:

300.13 Mechanical and Electrical Continuity - Conductors

(B) Device Removal. In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

I always tail where possible.
--
Zach


Jack_in_VA
Premium
join:2007-11-26
North, VA
kudos:1
Reviews:
·Millenicom

1 edit

said by Zach1:

said by alkizmo:

said by Speedy Petey:

Sorry, but this is NOT the "proper" way. It is one way.

What is the "proper" way? Or were you just saying that there is no one "proper" way?

If the circuit in question is NOT a MWBC, either feeding through the device and pig-tailing is generally acceptable. Some AHJ's require and some ECs prefer to pig-tail. For MWBCs, feeding through the device isn't allowed. Obviously, in the case of GFCI receptacles, you have no choice but to feed through if you are also protecting loads down-stream.

They don't have to be pigtailed on non MWBC circuits but:

the neutrals must be pigtailed on MWBC installation.

300.13 Mechanical and Electrical Continuity — Conductors
(B) Device Removal In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

Losing a neutral on a MWBC

Zach1
Premium
join:2006-11-26
NW Minnesota

said by Jack_in_VA:

They don't have to be pigtailed on non MWBC circuits but:

the neutrals must be pigtailed on MWBC installation.

300.13 Mechanical and Electrical Continuity — Conductors
(B) Device Removal In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

Posts and edits must have crossed. Since I don't usually feed-through, I had to find the text.
--
Zach


Jack_in_VA
Premium
join:2007-11-26
North, VA
kudos:1

I was doing an edit sorry


bigjoesmith

join:2000-11-21
Peoria, IL
reply to Jack_in_VA

I love that power point!


MaynardKrebs
Heave Steve, for the good of the country
Premium
join:2009-06-17
kudos:4
reply to alkizmo

said by alkizmo:

said by Speedy Petey:

Sorry, but this is NOT the "proper" way. It is one way.

What is the "proper" way? Or were you just saying that there is no one "proper" way?

The 'proper' way is whatever code says in your jurisdiction. Canadian & US electrical codes differ in some areas of practice.