Re: Why only 1 ground terminal and 2 hot/neutral on receptacles?

said by Jack_in_VA:

They don't have to be pigtailed on non MWBC circuits but:

the neutrals must be pigtailed on MWBC installation.

300.13 Mechanical and Electrical Continuity — Conductors
(B) Device Removal In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

Posts and edits must have crossed. Since I don't usually feed-through, I had to find the text.
--
Zach


Jack_in_VA
Premium
join:2007-11-26
North, VA
kudos:1

I was doing an edit sorry