 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | reply to tp0d
Re: sparkys- is it legal? Short answer is 'yes'.
You'd have to use a 60A disconnect with fusing to 15A, or, if you use a 30A disconnect, replace the upstream CB to no more than 30A. |
|
 tp0dyabbazooiePremium join:2001-02-13 Carnegie, PA kudos:4 | Ok so if I get a 60a rated disconnect with 15a fuses, its legal? Or mebe for temporary till the owners can get an electrician in there
Tnx
-j -- if it aint broke, tweak it!! currently on FiOS (kick aZZ!) |
|
 alkizmo join:2007-06-25 Pierrefonds, QC kudos:1 | reply to John Galt said by John Galt:You'd have to use a 60A disconnect with fusing to 15A, or, if you use a 30A disconnect, replace the upstream CB to no more than 30A. Curiosity: Why a 60A disconnect? The upstream CB protects the wire that goes to the disconnect, that wire is of proper gauge (If at 40A or lower). Anything connected downstream of the disconnect is protected by the 15A fuses. |
|
 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | You forgot protection for the disconnect...
Disconnects are rated for 30A or 60A...so those are the choices. You cannot put a 30A disconnect on a circuit protected at more than 30 amps. |
|
 leiboldPremium,MVM join:2002-07-09 Sunnyvale, CA kudos:6 Reviews:
·SONIC.NET
| reply to alkizmo said by alkizmo:Curiosity: Why a 60A disconnect?
While a fused 40A disconnect may exist as a specialty part, the next larger common rating is 60A (which will be easier to get). -- Got some spare cpu cycles ? Join Team Helix or Team Starfire! |
|
 MsradellP.E.Premium join:2008-12-25 Louisville, KY Reviews:
·AT&T U-Verse
| reply to tp0d said by tp0d:Ok so if I get a 60a rated disconnect with 15a fuses, its legal? Or mebe for temporary till the owners can get an electrician in there Tnx -j It's actually legal to leave it that way permanently if the owner wants as long as he doesn't need this circuit for something else. |
|
|
|