Re: Generator doesn't work with Power Vent Hot Water Heater

That would work so long as you are not connecting it to your house wiring.



GenNewbie

@rr.com

By that you mean back feeding the panel? I am not doing that.

I am currently running 1 new 10 gauge outdoor type extension cord. I would plan to use this new short GFCI cord between that cord and the generator to "protect" the connection. If that works, it would seem like $30 very well spent.


garys_2k
Premium
join:2004-05-07
Farmington, MI
Reviews:
·Callcentric
·callwithus

said by GenNewbie :

By that you mean back feeding the panel? I am not doing that.

I am currently running 1 new 10 gauge outdoor type extension cord. I would plan to use this new short GFCI cord between that cord and the generator to "protect" the connection. If that works, it would seem like $30 very well spent.

You'll be fine. The GFCI does add some peace of mind and protection, good idea. The N-G bond "jumper cord" enables it to work with your WH, that's fine, too. Good luck on your outage!


GenNewbie

@rr.com

Thanks very much. It will be great to have hot water and know that we are (mostly) safe. As always, I will be as safe as I can, use decent materials and try to be smart about things. I just never thought about the GFCI being in line in an extension cord. Genius!

I really appreciate the help!