Re: Indentify receptical

Thanks for the replies.

Aside from the outlet, and since the manual could be different, is there any way to determine max amperage for this circuit?

John Galt6
Forward, March
Premium Member
join:2004-09-30
Happy Camp

John Galt6

Premium Member

said by exocet_cm:

Aside from the outlet, and since the manual could be different, is there any way to determine max amperage for this circuit?

Circuit breaker rating...

leibold
MVM
join:2002-07-09
Sunnyvale, CA

leibold to exocet_cm

MVM

to exocet_cm
The manual states 16.7A for each of the two hot legs.

alkizmo
join:2007-06-25
Pierrefonds, QC

alkizmo to exocet_cm

Member

to exocet_cm
said by exocet_cm:

Thanks for the replies.

Aside from the outlet, and since the manual could be different, is there any way to determine max amperage for this circuit?

Full load amps @ 120 volts: 33.3
Full load amps @ 240 volts: 16.7

Now I'm betting they means 33.3A on 120v as in the total of the two legs.

So probably 15A breaker if they don't want the generator to die because of one leg being overloaded. 20A would be too much.