Re: Correct cable to run through conduit.

said by Mr Matt:

I was also wondering what wire gauge and type cable I should use if I want to install a 100 Amp circuit instead of a 50 Amp circuit.

I'll just comment on this part.

You dont want to be pulling #3 (for 100AWG) through conduit.
Jeezus Hard Christ it is!

Also, I don't see #3 fitting in a 50A generator inlet

Mr Matt

join:2008-01-29
Eustis, FL
kudos:1
Reviews:
·CenturyLink
·Comcast
·Embarq Now Centu..

According to the panel specification label I can install up to a 2 1/2 inch hub and conduit. I did not plan on running conduit across the attic but 4 Conductor jacketed cable. I was inquiring the correct type of cable to use. The conduit would only be to protect the cable until it passed through the soffit panel. If I ran a 100 Amp Circuit I would terminate the cable at the back porch in a small 100 Amp rain tight panel and install the 50 Amp breaker there and wire the inlet off that panel with #6 gauge conductors.