 alkizmo join:2007-06-25 Pierrefonds, QC kudos:1 1 edit | reply to John Galt
Re: Correct cable to run through conduit. said by John Galt:You looked in the wrong column... Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?
I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper). But I admit that table wouldn't apply once it's in the attic. |
|
 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | said by alkizmo:Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?
I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper). But I admit that table wouldn't apply once it's in the attic. The termination temp needs to be taken into account.
Generally speaking, all ampacities for "NM-type-ish" cables should be done from the 60 degree column. -- The most powerful weapon in the world is ignorance. Politicians exploit it to achieve almost anything they want.
|
|
|
|