Re: Correct cable to run through conduit.

said by John Galt:

You looked in the wrong column...

Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?

I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper).
But I admit that table wouldn't apply once it's in the attic.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:5

said by alkizmo:

Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?

I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper).
But I admit that table wouldn't apply once it's in the attic.

The termination temp needs to be taken into account.

Generally speaking, all ampacities for "NM-type-ish" cables should be done from the 60 degree column.
--
The most powerful weapon in the world is ignorance. Politicians exploit it to achieve almost anything they want.