Baseboard heater wiring questions

I have to install 2 new electric baseboards heater to replace the old one but after installing them it seem they don't produce not much heat which im asking if it's be because they are not getting 240V each.

Here is the wiring diagram so maybe i didn't connect the 2 wire correctly at the baseboard or it's the wiring ?


SparkChaser
Premium
join:2000-06-06
Downingtown, PA
kudos:3
Reviews:
·Verizon FiOS

if wired like the drawing and connected to 240V they should work. One caveat is, a lot of the stats I've seen from Honeywell formerly Aube (CA company) have a proportional output. If the set temperature is close to the room temp they won't put out full heat.

You might post of picture of what you have so others cans see and help.



dsa

@bell.ca

Click for full size
Thank you , this is what i have.


nunya
Premium,MVM
join:2000-12-23
O Fallon, MO
kudos:12
reply to dsa

If you don't have a VOM, go get one. Without a real voltage reading, everything is conjecture.
--
If someone refers to herself / himself as a "guru", they probably aren't.



dsa

@bell.ca

I have one.



nunya
Premium,MVM
join:2000-12-23
O Fallon, MO
kudos:12

Set the T-Stat above room temperature and measure the voltage at the heater. Report back.
--
If someone refers to herself / himself as a "guru", they probably aren't.



SparkChaser
Premium
join:2000-06-06
Downingtown, PA
kudos:3
reply to dsa

the voltage reading will be interesting since that doesn't look like a line t-stat.


Speedy Petey

join:2008-01-19

said by SparkChaser:

the voltage reading will be interesting since that doesn't look like a line t-stat.

I'm thinkin' the same thing.
Expand your moderator at work

resare

join:2012-11-07
Greenfield Park, QC
reply to Speedy Petey

Re: Baseboard heater wiring questions

+1...looks like a furnace (low-voltage) t-stat.



dsa

@bell.ca
reply to nunya

I measured at both and it's at 238V.



Cho Baka
Premium,MVM
join:2000-11-23
there
kudos:2
reply to dsa

Can you post the make and model # of the heaters and of the thermostat?

Also, are there any thermostats on the baseboard heaters themselves?
--
The talented hawk speaks French.



Dsa

@bell.ca

The model of the baseboards heater are LC4015W31 and the thermostat is RTH2310B.

There is no thermostats on the baseboard.

thank you



Cho Baka
Premium,MVM
join:2000-11-23
there
kudos:2
Reviews:
·TekSavvy DSL
·Cogeco Cable

1 edit

Can you post the maker names to go with those Model Numbers?

Is this the heater?
Dimplex Linear Convector LC series:

downloaddimplexlcinstr.pdf 322712 bytes


Is there any chance that the 2 heaters you have were inadvertently installed in series?

Do you have NO heat, or just very little heat?
Do you have a clamp-on ammeter you can use to measure current flow?


leibold
Premium,MVM
join:2002-07-09
Sunnyvale, CA
kudos:9
Reviews:
·SONIC.NET
reply to Dsa

said by Dsa :

The model of the baseboards heater are LC4015W31 and the thermostat is RTH2310B.


said by "Honeywell RTH2310B" :

Weekday/Weekend Programming - One program for the weekdays and a separate program for the weekends with 4 program periods per day
Energy Savings - Program to save up to 33 percent on annual heating and cooling costs (if used as directed, savings may vary depending on geographic region and usage)
Easy to Use - Basic operation keeps programming simple.
Backlit Display - Easy to read even in dimly lit rooms and hallways.
Early Start Function - Adjusts the pre-heating/cooling of your home so you are comfortable at your programmed times.
Filter Change Reminder
Works with heating and cooling systems
Does not work with heat pump systems and electric baseboard heat (120-240V)
1-Year Warranty

Unless there is also a 24V transformer and a relay/contactor involved, this thermostat is not suitable for your application.
--
Got some spare cpu cycles ? Join Team Helix or Team Starfire!


dsa

@bell.ca
reply to Cho Baka

Sorry , i posted twice and the original message didn't show .

It's a dimplex.

thank you



Cho Baka
Premium,MVM
join:2000-11-23
there
kudos:2
Reviews:
·TekSavvy DSL
·Cogeco Cable

1 recommendation

reply to dsa

Edit:

Is this your thermostat:
»yourhome.honeywell.com/home/Prod···310B.htm



--
The talented hawk speaks French.


dsa

@bell.ca
reply to Cho Baka

The baseboards model are Dimplex LC4015W31 , Thermostat is RTH2310B.

There is no thermostats on the heaters.

thanks



alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1

Dsa, the thermostat you are using won't work on baseboards. The end



dsa

@bell.ca
reply to Cho Baka

Yes it's that brand , no they are not there is 2 wire going to each baseboards , i only have a voltage tester model equus 4320a.

thanks



leibold
Premium,MVM
join:2002-07-09
Sunnyvale, CA
kudos:9
Reviews:
·SONIC.NET

1 edit
reply to dsa

Do your baseboard heaters have the low-voltage relay installed ?

It would be an optional part with Dimplex part numbers BLLVCxx or BLLVD.

This relay makes your DImplex baseboard heaters compatible with the Honeywell Thermostat but in that case your wiring would be different (and you still need a 24V power source, perhaps from an air conditioning system). The 240V line voltage should under no circumstances go to this particular thermostat!

Hopefully the instructions that come with the relay are better then those for the baseboard heaters (which could be much clearer).

Edit: ideally you should use a line voltage thermostat for your baseboard heaters. Are you using this thermostat just for the heaters or also to control a central air conditioning system ? If the thermostat is used to control both heating and cooling then using the low voltage relays from Dimplex is the way to go.
--
Got some spare cpu cycles ? Join Team Helix or Team Starfire!



LazMan
Premium
join:2003-03-26
canada
reply to dsa

Was the t-stat there and working before; or did you change it at the same time you changed the single baseboard unit out for the new ones?



dsa

@bell.ca
reply to dsa

Before it used to be an old thermostats like this one

»www.homedepot.ca/product/honeywe···g/903031

and the baseboard where 240V and there was no issues , then i changed for a thermostat like this RTH2310B 2 years ago and it was working well.

I then decided 2 months ago to replace them by dimplex 2 with the same wattage 1000w but 2 weeks ago they started to have this issue.

So now i though it was the baseboard so i went to change them and at the same time take 1500w which would cover the 300 square feet that i have , the issues still persist so i was wondering why suddenly what would be the problem.

Thanks



SparkChaser
Premium
join:2000-06-06
Downingtown, PA
kudos:3
reply to dsa

From Honeywell page

RTH2310B
Does not work with heat pump systems and electric baseboard heat (120-240V)



SparkChaser
Premium
join:2000-06-06
Downingtown, PA
kudos:3
Reviews:
·Verizon FiOS
reply to dsa

said by dsa :

Before it used to be an old thermostats like this one

»www.homedepot.ca/product/honeywe···g/903031

There's a relay somewhere.


leibold
Premium,MVM
join:2002-07-09
Sunnyvale, CA
kudos:9
Reviews:
·SONIC.NET

said by SparkChaser:

said by dsa :

Before it used to be an old thermostats like this one

»www.homedepot.ca/product/honeywe···g/903031

There's a relay somewhere.

Hopefully!

Keep in mind that all dsa said is that it was like the one he linked to (the link points to a low-voltage thermostat). Honeywell also makes line-voltage thermostats and in some cases they do look similar on the outside.

At this point a picture of the wiring at the thermostat (and ideally also at the baseboard heaters) would be really helpful because there is just too much left to guessing.

There may be a relay/contactor somewhere that was sized according to the load of the original baseboard heaters and whose contacts are now overloaded.
--
Got some spare cpu cycles ? Join Team Helix or Team Starfire!


dsa

@bell.ca
reply to dsa

It only control only the baseboard no ac on that.

As said before i had to use something similar due to the previous thermostat being a low voltage , i just wanted to be able to have different temperature at different time so that's why i changed the old one.

thanks



SparkChaser
Premium
join:2000-06-06
Downingtown, PA
kudos:3
Reviews:
·Verizon FiOS

1 edit
reply to leibold

I'm 99.99% sure that the round one never was a line stat. In fact I was using the round one for years on my electric heat with a relay. It used to be a mercury switch on a bi-metal spiral. Replaced last year.

My house is a T-stat museum. I have 6 different kinds. in 8 rooms.



dsa

@bell.ca

Click for full size
Click for full size
Click for full size
Here are the pictures , the thermostat was connected the same way the old was.


dsa

@bell.ca

I think also there is a relay since how would that wire would connect to the 240 V