Re: Poco infrastructure question

said by ArgMeMatey:

said by jack b:

This style meter is commonly used when supplying 2 phase service to a customer from a standard 3 phase 120/208V distribution system.

So phase-to-ground would be 120V and phase-to-phase would still be 208V, wouldn't it?

Exactly what we have throughout NYC, and likewise throughout many other cities. Its single-phase 208/120V power, not 'two-phase'.


ArgMeMatey

join:2001-08-09
Milwaukee, WI
kudos:1
Reviews:
·RoadRunner Cable
·AT&T Midwest
·voip.ms

said by whizkid3:

Its single-phase 208/120V power, not 'two-phase'.

Thank you. I was wondering how you'd measure 2 phases on a 120V meter. Getting confused with 240V grounded B phase.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:5

said by ArgMeMatey:

said by whizkid3:

Its single-phase 208/120V power, not 'two-phase'.

Thank you. I was wondering how you'd measure 2 phases on a 120V meter. Getting confused with 240V grounded B phase.

Is that delta...??

Or are you referring to a "high leg" system?


ArgMeMatey

join:2001-08-09
Milwaukee, WI
kudos:1
Reviews:
·RoadRunner Cable
·AT&T Midwest
·voip.ms

said by John Galt:

Is that delta...??

Or are you referring to a "high leg" system?

aka Corner-Grounded Delta. I just looked that up because I'm no expert. One transformer with three secondary taps. One tap (B) grounded. So A & C are 240V to ground.

Advantages:
- cheaper 2-pole gear can be used all down the line
- there are only three conductors just like split phase 240V
- B phase does not have to be (and CANNOT be) switched or fused.

But this is not what the OP has.

Also I ran across something on Wikipedia that mentioned that the old power station at Niagara Falls was two-phase. Maybe that was where I'd heard that before.
--
USNG:
16TDN2870
Find your USNG coordinates:
USNGWeb


whizkid3
Premium,MVM
join:2002-02-21
Queens, NY
kudos:9

4-wire, 3-phase 208/120 from a wye secondary on a transformer. Tie into any two phase conductors and the neutral, and you have single-phase 120/208. (Regardless of what they were doing in Niagara Falls ages ago.)