| reply to whizkid3
Re: Variable speed drive My furnace/AC is dumb, once the 'stat calls for cooling all three motors start at once (air handler, condenser fan and compressor). If a stepped time delay could be added I'd bet that not only would the lights not dim so much but (if I wanted to add one) a smaller standby generator would be needed to power it, too. |
|
 Zach 58Premium join:2006-11-26 NW Minnesota | said by garys_2k:My furnace/AC is dumb, once the 'stat calls for cooling all three motors start at once (air handler, condenser fan and compressor). If a stepped time delay could be added I'd bet that not only would the lights not dim so much but (if I wanted to add one) a smaller standby generator would be needed to power it, too. ICM has the timer you need to stage your equipment start-up. ICM is a common product line at most HVAC supply houses.
»www.icmcontrols.com/TIME-DELAY-R···ist.html -- Zach |
|
 garys_2kPremium join:2004-05-07 Farmington, MI Reviews:
·callwithus
·Callcentric
| said by Zach 58:said by garys_2k:My furnace/AC is dumb, once the 'stat calls for cooling all three motors start at once (air handler, condenser fan and compressor). If a stepped time delay could be added I'd bet that not only would the lights not dim so much but (if I wanted to add one) a smaller standby generator would be needed to power it, too. ICM has the timer you need to stage your equipment start-up. ICM is a common product line at most HVAC supply houses. » www.icmcontrols.com/TIME-DELAY-R···ist.html Thanks, yes, those are exactly what I'm talking about! |
|