brreaker

i have a breaker which has only 1 plug receptacle on it, the refrigerator and it keeps tripping, I put the refrigerator on another and it do not trip it. Any ideas?


Tig

join:2006-06-29
Carrying Place, ON
Reviews:
·voip.ms

Turn off the breaker, Inspect all visible portions of the wire for damage or discoloration. If no problems are apparent, replace the duplex receptacle. (cost $1)
If no fix, then next step is ; turn off the main breaker, replace the breaker (cost $10)
Edit; While you are in there, inspect the breaker to bus bar contacts for evidence of arcing. eg pitting, discoloration


nonymous
Premium
join:2003-09-08
Glendale, AZ
reply to banner

Is it a plain breaker, gfci or afci?



Camelot One
Premium,MVM
join:2001-11-21
Greenwood, IN
kudos:2
reply to banner

I agree with Tig See Profile. Obviously looking for any sign of wire damage is the first step. But most likely it is a bad connection at the outlet, a bad outlet, or a bad breaker. Any of which are cheap and easy to fix.



leibold
Premium,MVM
join:2002-07-09
Sunnyvale, CA
kudos:10
Reviews:
·SONIC.NET

1 recommendation

Did you put any nails or screws into walls lately (hung pictures, mounted cabinets/shelfs, etc.) ?
Driving a nail or screw through a hidden cable in the wall may go unnoticed at the time of the incident if the breaker trips quickly.
--
Got some spare cpu cycles ? Join Team Helix or Team Starfire!


garys_2k
Premium
join:2004-05-07
Farmington, MI
Reviews:
·Callcentric
·callwithus
reply to banner

I'm betting that the outlet's connected via a backstabbed connection. If it is, remove the conductors, clip off the ends of the wires that were backstabbed, strip a fresh 3/4" of clean wire and install it under the screws. The problem will likely cease.

Backstabs get loose and an intermittent connection on a motor load can easily trip a breaker due to the large inrush (and that goes even more for refrigeration compressors that restart too soon after shutting off).



incognito_2u

join:2005-03-15
Malverne, NY

said by garys_2k:

I'm betting that the outlet's connected via a backstabbed connection......

Agreed....had same issue only it wasn't a refrigerator, but a microwave........wired the feed via the screw terminals behind the outlet and never had a problem again.
--
"I'm an Analog guy in a Digital World!"