 | Onan generator runs at idel ONLY I have an Onan model 45.0EM It has set for years. I changed from Natural Gas to Propane. Unit will not get above an idel. Any suggestions? |
|
|
|
 Killa200Premium join:2005-12-02 Southeast TN | Did you have the unit modified on when you converted from Natural Gas to Propane? |
|
 alkizmo join:2007-06-25 Pierrefonds, QC kudos:1 | reply to Lost One That's not your generator's fault. As far as you're telling us, you haven't actually put it under load
SO IT IS YOUR FAULT! |
|
 | reply to Lost One said by Lost One :I have an Onan model 45.0EM It has set for years. I changed from Natural Gas to Propane. Unit will not get above an idel. Any suggestions? Probably a carburetor problem and or the governor is out of the loop. |
|
 PSWired join:2006-03-26 Annapolis, MD | reply to Lost One You'll want to post this at the SmokStak forums, where a ton of Onan experts hang out.
»www.smokstak.com/forum/forumdisplay.php?f=1
Troubleshooting will begin by manually moving the throttle while the engine is running, to see if the governor is holding it wide open and the fuel system is limiting engine speed, or if the governor is malfunctioning and not regulating at the correct speed. |
|
 | reply to Lost One Onan is up and running. Problem was lack of propane volume. Ran larger line and runs great. Thanks. |
|
 | reply to alkizmo Couldn't put unit under a load the unit would barely idel. |
|
 ropeguruPremium join:2001-01-25 Mechanicsville, VA | said by jimmylockwoo :Couldn't put unit under a load the unit would barely idel. Please, it is "idle" not "idel". |
|