Slant Fin Gas furnace - water dripping from overflow pipeMy 7 year old slant fin furnace has started to drip water regularly from the overflow pipe. I have to empty small bucket of water each day. Any suggestions on what's causing this and what I can I do fix it?
Thanks, Rob |
|
joe40 join:2005-11-26 Danbury, CT |
joe40
Member
2013-Mar-30 2:57 pm
if it hot water heat there too much pressure or a bad pressure release valve.
when hot check the pressure gauge
you said furnace so I am not sure what that can be |
|
|
garys_2k Premium Member join:2004-05-07 Farmington, MI |
to Rob J
Is this a hot air furnace, or a hot water boiler? |
|
jack bGone Fishing MVM join:2000-09-08 Cape Cod |
to Rob J
What does the pressure gauge on the boiler indicate the system pressure is? |
|
cdruGo Colts MVM join:2003-05-14 Fort Wayne, IN |
to garys_2k
said by garys_2k:Is this a hot air furnace, or a hot water boiler? Slant Air is a brand name of boilers and related hot water baseboard heaters. |
|
|
said by cdru:Slant Air is a brand name of boilers and related hot water baseboard heaters. That makes sense! (Thank you) |
|
tp0dyabbazooie Premium Member join:2001-02-13 Bulger, PA
1 recommendation |
tp0d
Premium Member
2013-Mar-31 12:01 pm
Your expansion tank is not doing its job, and the expansion in the system is causing the pressure to go over the normal 30psi, and drip from the relief valve.
If you have an old style air over water expansion tank, it needs purged of its water. If you have a new style bladder tank, it needs refilled with the proper charge of air.
Could also have a bad fill valve that isnt shutting off at the proper pressure, but thats less likely than the expansion tank.
If you dont know what I`m talking about, you need to call a professional. Your relief valve may also need changed, or boiler damage from pressure and fresh water can result.
-j |
|