[Electrical] Sparkies : Correct wire size for Heating unit ?

I am planning to install a 1000W linear convector:
www.homedepot.ca/product/1000w-l···e/963211)

With a simple thermostat to go along :
www.homedepot.ca/product/aube-no···t/977130)

My question for the sparkies : Is 14-2 wire going to work with this convector ? Will it be safe ? (Am asking the question, because i pre-wired with 14-2 romex (the wire is red) a couple of years ago while renovating and dont want to reopen up the walls...regret not running 12-2). The wires have been run for 5 years now, but never connected, as the room was an office, and now is becoming a bedroom (that needs more heat - for a newborn). Planning on installing a double 15 amp (240) square-d breaker for it. Nothing else would run on the wire. Run is about 60 feet from thermostat to panel.

Awaiting your input please sparkies



nunya
Who is John Galt?
Premium,MVM
join:2000-12-23
O Fallon, MO
kudos:10

1000/240 = 4.2A - well within the confines of 14/2.


resare

join:2012-11-07
Greenfield Park, QC
Reviews:
·ELECTRONICBOX

4 recommendations

Was hoping you'd chime in nunya .

Guy from home depot saying i will be fine : mmmh !
Nunya saying i will be fine : priceless !

Thanx, you put my worries to rest



tp0d
yabbazooie
Premium
join:2001-02-13
Carnegie, PA
kudos:5

you have a 15a double pole breaker, yes? havent seen one of those yet tho.. hrm

-j
--
if it aint broke, tweak it!!
currently on FiOS (kick aZZ!)


resare

join:2012-11-07
Greenfield Park, QC

Guess I chhose the wrong wording. I meant to say a 15 amp 240V breaker.



pike
Premium,MVM
join:2001-02-01
Washington, DC
kudos:3
reply to tp0d

said by tp0d:

you have a 15a double pole breaker, yes? havent seen one of those yet tho.. hrm

-j

Prepare to be.. shocked.

resare

join:2012-11-07
Greenfield Park, QC

Shocking indeed....
Now,tell me: where do i put my fingers in there (joke of course)

Seriously, thanx to all for the replies



mattmag
Premium,ExMod 2000-03
join:2000-04-09
NW Illinois
kudos:3

1 recommendation

reply to pike



I think I actually have one of those on the shelf that is 10A.



alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1
reply to resare

Double pole 15A breakers, found everywhere, after all, there are 15A MWBC.


resare

join:2012-11-07
Greenfield Park, QC

Thnx alkizmo.

Heading to HD tonite to get the breaker



LazMan
Premium
join:2003-03-26
canada
reply to resare

Standard "You can't do your own electrical legally in Qc" disclaimer goes here...

Make sure you get the right breaker for your panel - Square D has a few different styles... If you take the model number of your panel, they should be able to tell you what you need (most likely a QO type breaker, I'd guess...)


resare

join:2012-11-07
Greenfield Park, QC

Thnx for the tip. Will have my "electrician" install it for me then



alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1

said by resare:

Thnx for the tip. Will have my "electrician" install it for me then