Re: [Electrical] Wired a panel for the first time.

With side throw breakers the panel can be in either orientation and be compliant.

Zach1
Premium
join:2006-11-26
NW Minnesota
reply to Mango
No main lugs on the buss would be an indicator that the main breaker was factory installed. Your panel looks to be an Eaton/CH CPM120 or CPM120H with a factory installed 100A main breaker. If so, you don't need to do anything - your panel is approved for the intended application with the main breaker installed as is.
--