[Electrical] Looks like smart meters might act as surge protectors

»sacramento.cbslocal.com/ ··· r-surge/

garys_2k
Premium Member
join:2004-05-07
Farmington, MI

1 recommendation

garys_2k

Premium Member

[Electrical] Re: Looks like smart meters might act as surge protectors

That was a high voltage line coming in contact with a distribution line, likely not only fried all the meters but whatever was connected/plugged into the outlets of buildings fed from that leg. Big $$ down the drain.
Mr Matt
join:2008-01-29
Eustis, FL

Mr Matt to nibyak

Member

to nibyak
said by nibyak:

Looks like smart meters might act as surge protectors

I disagree. The smart meters may not have protected anything. Here in Lake County, Florida Power is transmitted via a 230,000 Volt line from power plants on the coast. Duke Energy Substations reduce the 230,000 Volts to 68,000 Volts where it is transmitted to Sumter Electric Cooperative Substations which reduce the voltage to 14,400 volts or 7,200 volts for delivery to the distribution transformers at businesses and residences. In our distribution system if a 68,000 volt line dropped on to a 7,200 volt line the. If there was no restriction the line voltage could have reached as high as 1,000 volts at 120 volt outlets and 2,000 volts at 240 outlets for an extended period of time.

garys_2k
Premium Member
join:2004-05-07
Farmington, MI

garys_2k

Premium Member

Yep, that kind of over-voltage would not be contained by a smart meter, even if it did explode (and the article said some people described its response as a "pop" and nobody said anything about the meter actually scattering its guts as shrapnel). Those over-voltages could just arc across anything that did try to open and keep the power going and going.

nunya
LXI 483
MVM
join:2000-12-23
O Fallon, MO
·Charter

3 recommendations

nunya to nibyak

MVM

to nibyak
There's going to be much bigger problems than the meters.
Electricians are going to be working overtime in that neighborhood. I hope Mr. Dumptruck had good insurance. I'll bet he didn't have enough to cover this mess.

I once witnessed a directional boring crew shoot through a secondary and then into a 4.8 kV primary. 3 houses started burning simultaneously. That boring company went out of business about 48 hours later.

Jack in VA
Premium Member
join:2014-07-07
North, VA

Jack in VA to nibyak

Premium Member

to nibyak
There's going to be a lot of Electronics and Appliances being replaced. When you see receptacle covers smoked is a good indicator.

LazMan
Premium Member
join:2003-03-26
Beverly Hills, CA

2 recommendations

LazMan to nibyak

Premium Member

to nibyak
I've seen a 7.2 kv shorted hard into the 240/120 distribution system... The local PUC had an up-fuck...

Cost them big bucks to fix and/or replace everything electical in about 7 houses, and a line-supervisor his job.

SunnyDays
join:2015-03-24
Ireland

SunnyDays to nunya

Member

to nunya
exactley
rody_44
Premium Member
join:2004-02-20
Quakertown, PA

4 edits

rody_44 to nunya

Premium Member

to nunya
Most directional drill companies carry inland marina insurance. Generally with 10,000,000.00 in coverage.

panth1
The Coyote
join:2000-12-11
Port Saint Lucie, FL

panth1 to nibyak

Member

to nibyak
Would be curious to know how power strip and/or whole house surge protectors held up to this.

tschmidt
MVM
join:2000-11-12
Milford, NH
·Consolidated Com..
·Republic Wireless
·Hollis Hosting

1 recommendation

tschmidt

MVM

said by panth1:

Would be curious to know how power strip and/or whole house surge protectors held up to this.

Probably not well - they are designed to shunt transients to ground not absorb the energy from a constant over-voltage condition long enough to trip breakers to isolate the fault. And if the fault current is high enough to trip the breaker the gap of an open breaker may not be large enough to quench the arc so current continues to flow even with the breaker tripped.

In many ways a power cross is worse then a lightning strike: long duration and differential mode rather then common mode. Lightning strikes tend to raise the voltage on both hot and neutral, so if a device is not connected to anything else it often is able to survive undamaged.

/tom

alphapointe
Don't Touch Me
MVM
join:2002-02-10
Columbia, MO

1 recommendation

alphapointe to nibyak

MVM

to nibyak

»youtu.be/lEAtWiUGeiA?lis ··· 51JCxPFw


I knew I had this one saved somewhere... I can't find the story on this any more, but I imagine a LOT of stuff was PF'd in this incident.

nunya
LXI 483
MVM
join:2000-12-23
O Fallon, MO
·Charter

nunya

MVM

»youtu.be/dRnwSmDWG0E


It was caused by Asplundh.
Mr Matt
join:2008-01-29
Eustis, FL

Mr Matt to panth1

Member

to panth1
said by panth1:

Would be curious to know how power strip and/or whole house surge protectors held up to this.

I do not believe surge protectors would not have prevented damage caused by the surge. More likely they would have started a fire. My Brother in Law owned a commercial cleaning and fire restoration company. One of his jobs was to clean up fire damage in several rooms of a large home. The homeowner had a whole house standby generator. The generator started up due to a power failure. Almost immediately all of the power surge protectors began melting and burning. It turns out that the generators output contained enough harmonic distortion to fry the surge protectors installed to protect personal computers.

Jack in VA
Premium Member
join:2014-07-07
North, VA

Jack in VA

Premium Member

I've always run my computers, tv's, Directv receivers etc on my Generator. Never any problem. I have surge protectors on the electronics.

PSWired
join:2006-03-26
Annapolis, MD

PSWired

Member

I've actually had this happen before. The voltage regulator on a standby generator went unstable due to UPSes dropping their load to the generator over and over. The voltage spikes that resulted from the oscillating voltage regulator overheated the MOVs in a power strip and burned the whole thing up (plus blew a 3 phase panel protector). I think I've posted pictures here before.

BGE had a similar incident in the county here a few years ago where some subtransmission lines crossed onto a distribution circuit. Same deal- all the appliances in the connected houses toasted.
TheMG
Premium Member
join:2007-09-04
Canada
MikroTik RB450G
Cisco DPC3008
Cisco SPA112

2 recommendations

TheMG to nibyak

Premium Member

to nibyak

Re: [Electrical] Looks like smart meters might act as surge protectors

About the only thing that will help with such an over-voltage condition is a means to automatically disconnect the incoming power when an over-voltage condition is detected.

Surge suppressors simply aren't designed to dissipate energy over a prolonged period of time, the components in the surge suppressor quickly overheat and burn up. They're designed to handle transients, which are often only microseconds in duration.

The automatic transfer switches for our generators at work have such a feature. Within a fraction of a second they open and disconnect power when an over-voltage condition is detected. This has actually spared equipment from expensive damages on a few occasions. Admittedly, none were quite as severe as what happened in that news article, nonetheless it is a nice added protection.
Mr Matt
join:2008-01-29
Eustis, FL

Mr Matt

Member

said by TheMG:

About the only thing that will help with such an over-voltage condition is a means to automatically disconnect the incoming power when an over-voltage condition is detected.

The only thing that might have saved the home electrical systems was a military spec circuit breaker I saw at a surplus store many years ago. It transferred the load to a ground bus when the breaker tripped. The biggest problem will be for customers that had their property destroyed, being attacked by various loss control weasels that will try to pay out a deprecated value for the damaged appliances rather than the replacement cost.
MaynardKrebs
We did it. We heaved Steve. Yipee.
Premium Member
join:2009-06-17

1 recommendation

MaynardKrebs to Jack in VA

Premium Member

to Jack in VA

Re: [Electrical] Re: Looks like smart meters might act as surge protectors

said by Jack in VA:

There's going to be a lot of Electronics and Appliances being replaced. When you see receptacle covers smoked is a good indicator.

And since we're all computer geeks here........

All the more reason to have at least some of your computer backups off-line and totally disconnected (ie. in a fireproof safe) at any one time or off-site.

Yes, that means you - Apple Time Machine fans, etc.... One good zap and there goes both your computer and your multiple Time Machine disks simultaneously. Data recovery from platters costs $1-10k depending on the breaks.

Jack in VA
Premium Member
join:2014-07-07
North, VA

Jack in VA to Mr Matt

Premium Member

to Mr Matt

Re: [Electrical] Looks like smart meters might act as surge protectors

said by Mr Matt:

The biggest problem will be for customers that had their property destroyed, being attacked by various loss control weasels that will try to pay out a deprecated value for the damaged appliances rather than the replacement cost.

They may be weasels but that's the way it works. You are not going to get replacement cost on contents. Home is covered if you pay the replacement cost rider.

Termites
@cox.net

Termites to nibyak

Anon

to nibyak
Who really cares about their meters how about the Damage done to these homes the wiring?

Lawsuit time..
ke4pym
Premium Member
join:2004-07-24
Charlotte, NC

ke4pym to nibyak

Premium Member

to nibyak
Is there any gear that would be worth a homeowner having installed to keep this kind of thing from burning down their house?

mackey
Premium Member
join:2007-08-20

mackey

Premium Member

No, any equipment that can stop several hundred amps at 7.2kv+ is $$$$$$$$$. The chances of it happening are so small you're better off with just generic insurance coverage.

battleop
join:2005-09-28
00000

battleop to garys_2k

Member

to garys_2k

Re: [Electrical] Re: Looks like smart meters might act as surge protectors

Something similar happened with EPB in the 90s. The difference was there was some sort of hardware failure that allowed the higher voltage lines to fall on the lower voltage lines. An entire neighborhood had most of the appliances and other items fried. A friend that knew some people that lived in that neighborhood said that EPB told the home owners it was their problem and not EPB's. I don't know how it eventually worked out but I'm guessing at some point in time some lawyers made out well.
battleop

battleop to alphapointe

Member

to alphapointe
That video gave me motion sickness....
Speedy Petey
join:2008-01-19

3 recommendations

Speedy Petey to nibyak

Member

to nibyak

Re: [Electrical] Looks like smart meters might act as surge protectors

Most news reports on this story are typical media over-dramatics.
The fact that the meters were "smart meters" was coincidental. With that kind of voltage surge a LOT of things went BOOM!
Merlin235
join:2014-10-14
USA

Merlin235 to TheMG

Member

to TheMG
A few years ago a squirrel shorted a high voltage line into our neighborhood's distribution network. My whole house surge protector tripped my main breakers which saved all my appliances and electronics. Some of my neighbors were not so fortunate.

The whole house protector was rated at 13,000 joules. Much more robust than a typical power strip surge protector. Not sure it would have helped in the situation on the video, but in this day and age a $100 for a whole house surge protector is inexpensive protection.
uniden9
join:2009-08-04
Birmingham, AL

2 recommendations

uniden9

Member

The problem with medium and high voltage is, even when the breakers have tripped, it can still arc across the opening. The breakers are not designed for infinite voltage range, but a much more specific one. High voltage is a nasty animal. It's also really cool how the insignificant capacitance rating of a regular wire at low voltage range, become very significant at higher voltages.

sk1939
Premium Member
join:2010-10-23
Frederick, MD

sk1939

Premium Member

Many breakers have a maximum rating (SquareD QO are 10kA) which means that at 1000V you get a maximum of 10A before failure I believe.
harald
join:2010-10-22
Columbus, OH

harald

Member

A little different than that.

10kA means that the breaker will interrupt up to a 10,000 ampere fault. This sort of rating became an issue when apartment complexes began to be fed with primary power to a step-down transformer located nearby the building. There's a code article that requires calculation of the maximum fault current and the provisions of breakers/fuses that can interrupt it.