JT, In this case it is pretty obvious that Comcasts drop was bonded (grounded) to the houses electrical system. The shield of the coax was able to carry enough current to keep the voltages within the house fairly stable. |
|
  Bobcat Premium join:2001-02-04 Bedminster, NJ | I'm still trying to understand the failure mode here. I agree it appears the neutral was open. But does it also require that the house was not grounded? |
|