Adding an inlet is a lot like a two pole outlet. You'll want to locate near where the generator will run, of course, and add an additional ground conductor split-bolted to your house ground to connect to your generator's frame ground terminal. Also, ideally, the generator won't have an internal neutral-ground bond.

Adding the interlock will take some drilling on the panel face, not a big deal, and yes, the 3 KW generator sounds like it will be fine. Any other motors besides the fridge? Sump pump, well, septic dosing?



Subaru
1-3-2-4
Premium
join:2001-05-31
Greenwich, CT
kudos:1

Nope really basic house it's from the early 1920's she has city water the only pump she needs to worry about is the tiny pump on her boiler.


garys_2k
Premium
join:2004-05-07
Farmington, MI

Then 3KW ought to be fine.



Subaru
1-3-2-4
Premium
join:2001-05-31
Greenwich, CT
kudos:1

yeah I think so too she only uses CFL's in the house and the two largest loads would be the fridge and microwave, I did not check the furnace pump but it's really tiny I'd be shocked if it was more then 1/2 HP.