Re: Correct cable to run through conduit.

said by kherr:

He wants to know what size CABLE to run for a 100 A sub panel .....

And I said 3AWG.

kherr
Premium
join:2000-09-04
Collinsville, IL
Reviews:
·Charter
I didn't see your post, sorry

Getting too involved in watching the Rams lose a game they could win for once ........ They're killing themselves with penalties


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:8
reply to alkizmo
said by alkizmo:

And I said 3AWG.

This is in error. The proper size is 1 AWG CU.

You looked in the wrong column...


nunya
LXI 483
Premium,MVM
join:2000-12-23
O Fallon, MO
kudos:12
Reviews:
·Charter
·voip.ms
·surpasshosting
I guess you are using an ECSBPK05?
You would use 6/3 for a 50A circuit, with the caveat that you need to check for voltage drop problems (probably not an issue). You shouldn't use NM cable in outdoor conduit. Use UF cable or individual conductors.
--
If someone refers to herself / himself as a "guru", they probably aren't.


alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1

1 edit
reply to John Galt
said by John Galt:

You looked in the wrong column...

Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?

I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper).
But I admit that table wouldn't apply once it's in the attic.

Mr Matt

join:2008-01-29
Eustis, FL
kudos:1
Reviews:
·Millenicom
·Embarq Now Centu..
·Comcast
·CenturyLink
reply to nunya
nunya, you are correct I have a Siemens ECSBPK05 interlock and a 50 Amp two pole circuit breaker which I have yet to install. I am trying to determine the cost of 6/3 UF with ground in 100 Foot lengths. During my search for UF I found a lot of 50 Amp extension cords from 15 feet to 100 feet long in the Recreational Vehicle section of Amazon.com. The plug and receptacle are the same as a 50 Amp Electric Range cord set. I saw a picture of a 50 Amp inlet using the same kind of plug but I have not been able to find a surface mount weather resistant version. I might decide to install the inlet next to the service entrance panel and use a 50 Amp extension cord to connect the service panel to the 50 Amp receptacle on the generator. I appreciate your advice.


John Galt
Forward, March
Premium
join:2004-09-30
Happy Camp
kudos:8
reply to alkizmo
said by alkizmo:

Not arguing, just curious for my own education: Which table & column should I be looking at for this situation?

I'm looking at Table B.310.15(B)(2)(1) over the 90C rating (copper).
But I admit that table wouldn't apply once it's in the attic.

The termination temp needs to be taken into account.

Generally speaking, all ampacities for "NM-type-ish" cables should be done from the 60 degree column.
--