| Backfeed breakers ... are they the same ..... ..... as a regular breaker (Square D is my brand) ?? Or do they make special breakers (never have seen any listed, but it's not like everyone would need one). HD finally got the generator I was looking at back in stock a town over and have some time to devote to the cause ......
Be Prepared !! |
|
 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | If the breaker is NOT labeled with "line" and "load", it is suitable for backfeeding. |
|
 kherrPremium join:2000-09-04 Collinsville, IL | I figured that, but better to ask. Thanx |
|
 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | No problem.
For molded case CBs, the issue is solely one of labeling rather than any functionality. |
|
 leiboldPremium,MVM join:2002-07-09 Sunnyvale, CA kudos:6 Reviews:
·SONIC.NET
| reply to kherr For residential use, Square D makes loadcenters (breaker panels) for QO series breakers and HOM series breakers (they are not interchangeable).
When using a plugin-style breaker (QO and HOM both are) as backfeed breaker then a retaining kit is required to hold the breaker in place (prevents the breaker from popping out of the panel bus). This also applies to most other brands of residential breakers.
A retaining kit is not needed for bolt-on breakers (such as Square D QOB breakers) which are more common in commercial/industrial applications.
Edit: fixed spaces in URL -- Got some spare cpu cycles ? Join Team Helix or Team Starfire! |
|
 kherrPremium join:2000-09-04 Collinsville, IL | I'm QO all the way. The retaining kit came today and stated to use with "backfeed breakers only", hense the question. |
|
 John GaltForward, MarchPremium join:2004-09-30 Happy Camp kudos:5 | reply to kherr Retainers are required any time you use any CB other than a "integral main" for connection to the power source.
The intention is to keep it from dislodging during a fault event.
Say you have a "main lugs only" panel, but want to have a "local" main CB for a disconnecting means. You would then need to install a retaining bracket. |
|
|
|
 leiboldPremium,MVM join:2002-07-09 Sunnyvale, CA kudos:6 Reviews:
·SONIC.NET
| reply to kherr The only limitations regarding backfeeding that I could see were:
- QO-GFI (combination circuit breaker GFCI) should not be used as main breaker or backfeed breaker. - Some Square D panels with 100A main breaker can only be used with backfeed breakers up to 70A.
You should be fine with any standard 2-pole QO breaker. -- Got some spare cpu cycles ? Join Team Helix or Team Starfire! |
|