Hot Water Runs Out Quickly: What's Wrong With My Water Heate

The hot water runs out really quickly all of a sudden. It just started a few days ago. I can only get about 3 inches in the tub before it goes cold. Before, I could take a 20-minute shower. I have an '01 Craftsmaster (gas). I've heard about dip tubes going bad, but I don't think that applies to this model. Any ideas?



jack b
Gone Fishing
Premium,MVM
join:2000-09-08
Cape Cod
kudos:1

It applies to all tank-type heaters.

That heater (12 yr old? ) is on borrowed time. Don't even bother trying to fix it.
--
~Help Find a Cure for Cancer~
~Proud Member of Team Discovery ~



alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1

you have a defective element.



shdesigns
Powered By Infinite Improbabilty Drive
Premium
join:2000-12-01
Stone Mountain, GA

said by alkizmo:

you have a defective element.

On a gas water heater?


alkizmo

join:2007-06-25
Pierrefonds, QC
kudos:1

is there such a thing? (in multiples i mean)
only reason he'd have SOME hot water.


garys_2k
Premium
join:2004-05-07
Farmington, MI
reply to elanp

Why don't you think you have a broken dip tube? Your symptoms, very little hot water, are exactly right for that problem.



elanp

@myvzw.com

Supposedly, dip tube problems are only with water heaters built in 1993-97.



jkj860
The Final Frontier

join:2002-01-10
Valparaiso, IN
reply to elanp

I would agree with garys_2k on the dip tube. Seems obvious but check the temp setting. Mine got moved once and that was the last thing I looked at.
--
I know you think you understand what you thought I said, but I am not sure you realize what you heard is not what I meant. Nixon



tp0d
yabbazooie
Premium
join:2001-02-13
Carnegie, PA
kudos:5

Some newer dip tubes have a closed end... If there is something in the end of the tube clogging it, it can cause cold water to spray in a different direction, dropping the temperature of the tank..

Its rare to see a tube fall off, but its possible.. Only way to be sure is to take out the cold fitting, and check the tube by removing it with a set of needlenose.

I`d check for a cross connect first.. Turn off the cold valve feeding the heater, and make sure the hot pressure stops flowing. If it doesnt, you have cold water getting into the hot system somewhere, which will also drop the temp..

-j
--
if it aint broke, tweak it!!
currently on FiOS (kick aZZ!)


garys_2k
Premium
join:2004-05-07
Farmington, MI
Reviews:
·Callcentric
·callwithus

1 recommendation

reply to elanp

You can also look inside by draining the tank and removing the drain fitting. If you can see the bottom of the dip tube resting on the floor of the tank (looking into the small hole left by the drain fitting, use a good, small mag light and get up close) then it's broken at the top.

If that's the case you have three choices: replace the tank (it is 12 years old), replace the dip tube (can be a bitch to get that fitting off and trying to remove it may permanently damage the tank) or feeding the inlet water into that drain fitting port. The last would be more of a plumbing project but it does work and you'll have no more dip tube issues. Your choice.



elanp

@myvzw.com

I bought a dip tube and read a bunch of articles on how to replace one, but I'm at a bit of a conundrum at the first steps. I turned the cold water off and put the temp on the lowest setting without turning off the pilot. The thing is: I tried to run hot water into the tub to empty the tank and maybe even get a hot bath out of the deal, but nothing comes out. The cold water, however, runs freely. That doesn't make sense to me. Is it safe for me to even proceed in trying to take the top off?



Steve
I know your IP address
Consultant
join:2001-03-10
Yorba Linda, CA
kudos:5

3 recommendations

reply to elanp

Did you have a sudden increase in the number of females in your home? This is highly correlated with reduced availability of hot water.



rjackal
Premium
join:2002-07-09
Plymouth, MI
reply to elanp

You're misunderstanding how the hot water system works. You need the cold water ON in order to provide the pressure for the hot water to come out of the tank.

The only way to drain the tank with the cold water OFF (i.e. without refilling the tank) is to use the drain valve on the bottom of the tank.
Hopefully you have a functioning floor drain near the tank, and a length of garden hose to get from the tank to the drain. Open a nearby hot water faucet to let air back in to the system so it will drain faster.

I'm thinking you should call a plumber, though.



Jtmo
Premium
join:2001-05-20
Novato, CA
reply to elanp

Check your faucet aerators for bits of debris, that would be you dip tube gone if it is metal or plastic. If you have hard water, it could just be minerals.
The problem with putting in a new dip tube is you must have head room over the water heater that equals the length of the water heater. The bigger issue is the old tube is still lying on the bottom adding bits of plastic to your water supply.
So, if the dip tube is gone, new water heater since yours is 12 years old. Disconnect the cold supply to find out.

»www.ronhazelton.com/tips/faulty_···lacement



tp0d
yabbazooie
Premium
join:2001-02-13
Carnegie, PA
kudos:5

From what Ive seen, you should NOT be attempting this.

Repairs always cost more after the homeowner fucks it up.

just a warning

-j
--
if it aint broke, tweak it!!
currently on FiOS (kick aZZ!)



The E
Please allow me to retort
Premium
join:2002-05-26
Burnaby, BC
reply to elanp

What he said!! ^^^^^

Why bother repairing a 12 year old water heater? It's almost certainly ready to rust-out and spew rust or worse, leak all over your home.

Also, if you're not aware of how the basic plumbing in your home works, are you sure you want to mess with the tank? Seems perilous!



mityfowl
Premium
join:2000-11-06
Dallas, TX

+1