Re: Residential fire sprinklers, inspection needed?

said by covid:

I just did flow test of the system. After 1 minute, the reading was at 190 psi. What concern me is the alarm bell never went off. I thought that it is supposed to go off?

If you have a flow switch that bell should be ringing.

A flow switch is a red box mounted to the side of the main pipe feeding the sprinkler system, with copper pipe it is normally installed a larger section of pipe using a tee, when water flows past it's paddle it closes a switch activating the bell.

I don't have one in the shop but that is what they look like just smaller for residential.




Now you might have a pressure drop switch in place of a flow switch, it detects the normal pressure drop of a head activating and closes a contact when that happens.

This is what a pressure switch looks like.







If you want to inspect either one post back a picture and I will lead you through how to do that.
covid
join:2020-05-24

covid

Member

said by Well Bonded:

said by covid:

I just did flow test of the system. After 1 minute, the reading was at 190 psi. What concern me is the alarm bell never went off. I thought that it is supposed to go off?

If you have a flow switch that bell should be ringing.

A flow switch is a red box mounted to the side of the main pipe feeding the sprinkler system, with copper pipe it is normally installed a larger section of pipe using a tee, when water flows past it's paddle it closes a switch activating the bell.

I don't have one in the shop but that is what they look like just smaller for residential.

[ATT=1]

Now you might have a pressure drop switch in place of a flow switch, it detects the normal pressure drop of a head activating and closes a contact when that happens.

This is what a pressure switch looks like.

[ATT=2]

[ATT=3]

If you want to inspect either one post back a picture and I will lead you through how to do that.

Yes i have that, when relief pressure valve is open, it will ring after 60 seconds.

Well Bonded
join:2015-10-17
Labelle, FL
·T-Mobile

Well Bonded

Member

said by covid:

Yes i have that, when relief pressure valve is open, it will ring after 60 seconds.

That's the proper way to do it, the 60 second delay is known as a retard, it's purpose is to prevent the flow from ringing the bell due to water surges.

If you opened the flow you will see a knob marked retard, it controls a diaphragm that holds back the lever that activates the switch, commonly it can be set from 0 to 120 seconds, the ones I install I set for 30 seconds, that's enough to prevent false trips and soon enough to get someone quickly alerted about the sprinklers going off.

Fire is a mean thing, I don't know if it is true but I have been told a fire will double in size every 60 seconds it's burning, so literally seconds count and that's where both properly installed smoke detectors and sprinklers can save lives.

And sprinklers while causing a lot of water damage, can suppress a fire early on reducing property damage compared to leaving the fire unchecked until the FD arrives.